Have any of you ever come across a TT system that the earth fault loop impedance readings are as good as a TN, TNC-S system?

Ie, falling well within the maximum permitted value of the MCB?

If so, would you then still recommend RCD protection, If there is none?

Cheers
 
E54 may very well have come across it but I've only ever achieved an Ra of just under 4 ohms so had to fit additional RCD protection anyway.


What type of install do you have this reading on??? multiple rods, mats, tapes etc???
 
Its nice to see such a low reading however if they can plug an ext lead into the downstairs sockets to use outside it has to be protected by an RCD and as good workmanship plus the low cost of RCD's its a no brainer I would fit one.
 
If main bonds not excluded from the test, could it be picking up the earthing off next doors gas/water.

I had one job on a TT out in the sticks, the supply originated from a shed next to the overhead supply pole, I too had a reading of 0.25 which i thought was good for a TT. Fast forward 3 years and customer trenched next to supply shed only to find my earth rod had crashed into the boards earth rod about three metres away from the pole which we did not know was there.
 
Only seen this once, the property was in a remote location with it's own private metallic water supply pipe which was used to earth the installation under the 15th edition regulations.
 
Once got 0.29. I couldn't believe it ,I had to triple check then check calibration cert when I got home and I still checked again using another meter the following day
 
It is not domestic, it is a special location and Industrial. The system is supported by Rods/Mats and Tape The Ze value is 0.03 ohms.

Having tested and inspected countless TT systems i have never ever seen anything like this.
 
I doubt they could carry out such a request! the supply is direct from 11/500v - 400v transformers. It would cost a fortune!

ha ha
 
It is not domestic, it is a special location and Industrial. The system is supported by Rods/Mats and Tape The Ze value is 0.03 ohms.

Having tested and inspected countless TT systems i have never ever seen anything like this.

That's because someone for a change, has done things properly, someone that understands what it takes to create a good TT system. Very easy in salt marshlands a bit more difficult elsewhere but very much achievable, as you have just found yourself!!!
 

Reply to TT System questions in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
916

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K
  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
699

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top