i got the local electric compant to convert it to pme for nothing that must be better !!!!!!!!!!!!!!!!!!!!!

Please explain how a PME supply would be better for this industrial site?? You have a ''True Earth'' with a Ra value of .03 ohms. You can throw out all special tripping times imposed on a typical UK TT system!!!

Mind, i would be a little doubtful myself at that .03 ohm reading, but i could well believe a .30 ohm value, that is very much achievable in a good resistivity soil area...
 
Yeah there is a lot of planning gone into the setup of the site, there is tape, mats and rods with some interconnected via each other.

My question remains though does it still require a time delayed main switch back at the point of origin? even though values are met?

I personally think that yes the requirement is still needed, but would it be beneficial to start fitting RCBO to every final circuit?an industrial special location it is something i have never seen before.

In a domestic scenario not a problem, or in an agricultural scenario too. But the fact that this is an industrial site i am not 100% sure

the joys of TT

ha ha
 
Last edited by a moderator:
With Ra levels that low (and i do still doubt .03 ohms) that is proven stable, why would you be making special considerations that are based on Ra's of around 200 ohms??


I hope when you tested this extensive TT system you used a dedicated earth tester, and not relied on your MFT. and that your test spikes were placed outside any Zone of influence?? Otherwise your test results would be considered to be unreliable and be probably incorrect....
 
Do remember that they are documents from the US DoD and so are for information only, if BS7671 or other documents differ then the UK standards must be followed.
 

Reply to TT System questions in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
919

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K
  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
699

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top