Engineer54
That's not an Ra value is it?? Perhaps i should have asked for the existing Ze value!! lol!!
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss TT system sub main design in the Talk Electrician area at ElectriciansForums.net
Thanks for the quick replies, the garage is detached and only three meters away the supply circuit is to be buried and will only be about 6m long. The SWA will not run through insulation save for about 60mm.
rattlehead, are you saying the 100mA S type will cover the sub main and I should use a 60898 cb in a way separate from the 30mA part of DB1?
Ask the local power network operator if you can have it PME'd to begin with. Many are doing so free of charge now.
All this 'do you don't you add an extra rod' is splitting hairs really. Personally i would do it mainly to try and further reduce down the Zdb value in the garage. Also by adding an extra rod you are not relying on connecting the earthing conductor from the house to the shed and using that as a combined earthing and bonding conductor. Bare in mind if you use only the rod from the house supply you would need to run your bonds from the garage back to the M.E.T within the house or ensure your earthing conductor is big enough to use as a combined earthing and bonding conductor.
Thanks, I was feeling a bit bullied there for a moment. It is only a small part of the question, well actually it wasn't any part of the original question, I do like to make it correct though and as the existing rod hasn't got an earth pit I think I will put it in. As far as PFC not being Ra, no it's not but it is quite easy to divide by the voltage which makes the Ra 115 ohms-ie less than 200
know what you mean did however manage to drive a 2.4m rod in at a job in the middle of dartmoor the other day and got Ra of 22 ohmsMust be nice to live somewhere where you can drive a 2.4M rod in without there being a resounding clang as it hits bedrock at 500mm. Trust me to always live at the top of a hill (I have a fear of drowning).
Must be nice to live somewhere where you can drive a 2.4M rod in without there being a resounding clang as it hits bedrock at 500mm. Trust me to always live at the top of a hill (I have a fear of drowning).