Shop with no earth coming from head, overhead lines in sight everywhere - definitely no earth from the DNO.
Two 10mm earths going into the DB. One going to the water and another which disappears through a wall somewhere heading towards an external area never to be seen again.
Customer doesn’t know where the earth rod is located (if there is one).
Took an earth loop reading at the board and tester shows 0.41ohms with water bonding disconnected.
How??!!
Work required at the store but don’t want to agree unless this reading can be verified as legitimate somehow or the customer agrees to a new rod being installed.
Two 10mm earths going into the DB. One going to the water and another which disappears through a wall somewhere heading towards an external area never to be seen again.
Customer doesn’t know where the earth rod is located (if there is one).
Took an earth loop reading at the board and tester shows 0.41ohms with water bonding disconnected.
How??!!
Work required at the store but don’t want to agree unless this reading can be verified as legitimate somehow or the customer agrees to a new rod being installed.