Hi guys got a small problem with a tt, never come across it before and hope to never again. About a foot below the soil is solid rock however i've managed to get two rods in the ground at a couple of points using the kango hammer, the reading is still 320 ohms:eek:, any tips on what to do in this situation, is there another means of earthing that is easier to get in the ground with the rock the way it is? distributors earth is not an option as its a steel outbuilding remote from the supply head:( every tt i've done has been fine, some rocky ones but always able to get a good reading, sooooo frustrating
 
Does it have to be a tt system?
What is the earthing arrangement of the main supply, how far to your outbuilding and what have you run to it?
 
Does it have to be a tt system?
What is the earthing arrangement of the main supply, how far to your outbuilding and what have you run to it?

Tncs , its probably 50m and there is a building inbetween so this is coming off that which is connected to the main earth but there's no conductive parts in that one, but this whole building is steel so i don't want two different potentials
 
The reason that you normally need a tt supply to outbuildings is that on any installation there is only one main earth terminal so any outbuildings with extraneous conductive parts will need an equipotential bonding conductor going back to the met and this can often mean a main bonding conductor of a larger size than the live conductors and it is easier to make it a tt system.

You have a 16mm 3 core going to your outbuilding, so as long as your main bonding conductors going to your met do not have a greater csa you can use the third core of your armoured as a combined cpc/main bonding conductor.
 
Hi guys got a small problem with a tt, never come across it before and hope to never again. About a foot below the soil is solid rock however i've managed to get two rods in the ground at a couple of points using the kango hammer, the reading is still 320 ohms:eek:, any tips on what to do in this situation, is there another means of earthing that is easier to get in the ground with the rock the way it is? distributors earth is not an option as its a steel outbuilding remote from the supply head:( every tt i've done has been fine, some rocky ones but always able to get a good reading, sooooo frustrating
hi there , the first question i would ask is, when you put the first earth rod in what reading did you get. when installing the secondary rod in did the reading go down, if so carry on putting more rods in until less than 200 ohms. if this dont work , maybe you might be better putting an earth plate in instead as not like a rod where you aim for depth, a plate will spread accross the ground instead. good luck
 
On second thoughts though, is it not possible to use the combined csa of you armour and 3rd core as a bonding earthing conductor? thus continuing the PME, I don't like the sound of your soil conditions and would not personally leave it as a TT with those readings! Look at it now its wet! what will it be like in next summers inevitable 'heatwave'?
 

Reply to TT system in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
202
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
983
  • Question
The issue I was having turned out to be a faulty transformer on the pole 30m away... after hassling the northern powergrid (and having then visit...
Replies
9
Views
989

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top