On second thoughts though, is it not possible to use the combined csa of you armour and 3rd core as a bonding earthing conductor? thus continuing the PME, I don't like the sound of your soil conditions and would not personally leave it as a TT with those readings! Look at it now its wet! what will it be like in next summers inevitable 'heatwave'?

50 M isn't that far for a 16mm cable. use the 3rd core as your bonding conductor and the armour as the CPC.
What your talking about, would only affect a situation where the 3rd core wasn't of a suitable size to fulfil bonding CSA requirements, and then relying on the armouring to make-up the shortfall!! Not the case here, looking at it only at face value that is... lol!!!
 
Take an Ra reading off the metal frame of the building. If it's got good foundations - might just do.

Although I totally agree with you and personally see it as the best possible means of gaining a very respectable Ra .

However after a discussion with another contractor on the subject about 2 months ago , we enquired with the ECA technical about if it was permissible to use a steel framed building as essentially a means of a main earth and were unequivocally told no !
So i would imagine the same rule would apply to using the frame as a means of helping to lower the Ra to a more acceptable level !?
 
Although I totally agree with you and personally see it as the best possible means of gaining a very respectable Ra .

However after a discussion with another contractor on the subject about 2 months ago , we enquired with the ECA technical about if it was permissible to use a steel framed building as essentially a means of a main earth and were unequivocally told no !
So i would imagine the same rule would apply to using the frame as a means of helping to lower the Ra to a more acceptable level !?

Interesting ...... Can't think of a reason why they would say that, unless the building you were discussing already had a pme or multiple pme supplies, or something along those lines.

Surely the connection to earth under a building with driven piles and/or sitting on a reinforced concrete slab would be better than an earth rod that can only be driven half a meter into the ground.
 
Last edited:
No it was a cattle barn in the middle of others and all TT , I can not for the life of me see why it would be unacceptable but he was adamant about it , i think he may have even quoted some reg numbers as well , but alas my memory is about stuffed nowadays !

But then as a thread from a few months ago in which i think Lenny or Engineer54 pointed out , you are allowed to use structural steels as a main bonding conductor to say your gas or water at the other end of a building , but not as a main earth ?
 
No it was a cattle barn in the middle of others and all TT , I can not for the life of me see why it would be unacceptable but he was adamant about it , i think he may have even quoted some reg numbers as well , but alas my memory is about stuffed nowadays !

But then as a thread from a few months ago in which i think Lenny or Engineer54 pointed out , you are allowed to use structural steels as a main bonding conductor to say your gas or water at the other end of a building , but not as a main earth ?

Even stranger then.

Structural steel is OK to use as a main bonding conductor, although I think they were talking about buildings that already had a TN supply, but in this case the Bonding/Main earthing conductor would be combined. I wouldn't have a problem using the building as a TT earth if it was possible to get a better Ra value than the rod.

Perhaps your man at the ECA was having an off day, don't we all lol.
 
No it was a cattle barn in the middle of others and all TT , I can not for the life of me see why it would be unacceptable but he was adamant about it , i think he may have even quoted some reg numbers as well , but alas my memory is about stuffed nowadays !

But then as a thread from a few months ago in which i think Lenny or Engineer54 pointed out , you are allowed to use structural steels as a main bonding conductor to say your gas or water at the other end of a building , but not as a main earth ?

Depends whether the steels have been driven into the earth, or are connected to a Ufer earth, whether it will be a good earth or not. You need to check/test first...

Other than that i'm afraid your man from the ECA is talking out of his rear end, as to not being able to use such a system as your TT earthing !! ...lol!!!
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
TT system
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
21

Advert

Thread statistics

Created
monkeyelectric,
Last reply from
Engineer54,
Replies
21
Views
4,181

Advert

TrueNAS JBOD Storage Server

Back
Top