Peter Woodford

Guys,

been asked to do a cu change on a tt system i know it has to have a split load board but does it still need the main switch what i can remember it does'nt.

thanks
 
Guys,

been asked to do a cu change on a tt system i know it has to have a split load board but does it still need the main switch what i can remember it does'nt.

thanks

The main switch is required for all installations irrelevant of the earthing system
You may be refering to the time delay requirement that was often needed under the 16th edition

This requirement is obsolete because all circuits now require 30 m/ampRCD in a TT installation so it would be a waste of money puttiing in a time delay rcd
It doesn't have to have a split load board,you could use rcbos or do as I and use a split load with 30 m/amp rcd for sockets shower cooker and whatever else and rcbos for the lighti

Using large cables for the rod in a TT system is less of a worry than TN systems
The rcd will need only 30 m/amp to operate, so the earth cable is unlikely to carry a large fault current for any noticeable period unlike a TN systekm fault
4mm would probably be adequate for any TT installation, allthough the recomended will indicate larger sizes
 
Last edited:
Is it me or do you need minimum main CPC not less than half CSA of incoming line conductor, but min of 16mm? table 54.7

If you read 542.3 it tells you that the earthing conductor shall comply with section 543
Also if its PME then it shall also meet 544.1 so

Section 543 says it can be selected in accordance with 543.1.4 where it says it can be determined by table 54.7

The other option it gives is to use the calculation in 543.1.3
the adiabatic equation
For a system with a 30 m/amp rcd the size of cable to carry the very low required fault current is very small
It can be as low as 2.5mm if its protected or 4mm if its unprotected

If it is buried in the ground table 54.1 would apply where 16mm would be required for unprotected buried cable

Although these small conductor sizes can comply,I myself generally use 10mm for TT systems,but there are systems with smaller sizes being used out there and there is no problem people using them

So on PIRs do not be too hasty to condemn those installs
 
thanks for the intel des but there was very little info on how guy was going to have a CPC to rod so i was basically being ballpark but safe, i was always told to have at leats half csa for your earth to line, regardless of of earthing system. but thanks anyway sorry Mac ive always just put in 16mm min.
 

Reply to tt system in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
808
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

Also use a tails gland and clamp if available and make sure tails are secured to a wall. The danger here is a live to earth fault in the Consumer Unit
Replies
7
Views
574
It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
2
Replies
18
Views
712

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top