G

Grant M

I recently changed a fuse box and began testing to discover the property has no earth. I put an earth rod down and my Ze is 49ohm, which is an acceptable figure according the the 17th, which requires less than 200ohm. How do my Zs readings work? I am measuring about 12ohm on the socket circuits. All circuits are RCD protected. Do I just accept these high readings compared to TN systems, is this normal? Another question I have is what size earth cable should be used?

This is only the second time I have installed an earth rod, the first being for a temp supply.

Regards,
GrantM.
 
I recently changed a fuse box and began testing to discover the property has no earth. I put an earth rod down and my Ze is 49ohm, which is an acceptable figure according the the 17th, which requires less than 200ohm. How do my Zs readings work? I am measuring about 12ohm on the socket circuits. All circuits are RCD protected. Do I just accept these high readings compared to TN systems, is this normal? Another question I have is what size earth cable should be used?

This is only the second time I have installed an earth rod, the first being for a temp supply.

Regards,
GrantM.

Grant, your maximum Zs readings (assuming 30mA RCD protection) will be 1667 Ohms.

Obviously in a domestic situation, you will know from R1+R2 values that your continuity of protective conductors test readings are adequate.

Will your earthing conductor be buried and if so mechanically protected?
 
Grant, your maximum Zs readings (assuming 30mA RCD protection) will be 1667 Ohms.

Obviously in a domestic situation, you will know from R1+R2 values that your continuity of protective conductors test readings are adequate.

Will your earthing conductor be buried and if so mechanically protected?

Thanks for reply.
No, the earthig conductor will not be buried.
 
the reason your Zs readings are less than your Ze is because the bonding to the water/gas is providing a parallel path, thus effectively reducing your Ze.as IQ said, your max value for Zs to enter on the test results is 1667 for all circuits, regardless of the MCB type and rating. your main earth cable can be 6mm , however i prefer to use 10mm if not mechanically protected.
 
I try to called the supplier to see possibility of getting a tnc-s system,
Problem here is that if there is an adiquate means of earthing at the install (consumers TT) they are likely to charge the consumer to put a service head in with a neutral link (if it doesn`t have one already).............Dont forget, the DNO is only responsible for earthing their own supply cables/systems and have no obligation to a consumer other than the supply is safe to use and adiquate for the expected load (within reason).....
 
Surely with the regs stating unless designated circuit (cable more than 50mm in building fabric) or have skilled person permanently onsite etc then 99.9% of the time circuits should be protected by RCD, with a sky high zs the surely nuscience tripping is a problem, these rcds are mega sensitive, so there has to be some responsibility somewhere along the line for the earthing..... Its amazing the size and man power of these distributors but soon as you mention a earth system to them they shy away from it and leave it to a man with hammer and a rod!
 
Going forward at least all new installs must be given an earth by the DNO:

ESQCR 24:
(4) Unless he can reasonably conclude that it is inappropriate for reasons of safety, a distributor
shall, when providing a new connection at low voltage, make available his supply neutral conductor
or, if appropriate, the protective conductor of his network for connection to the protective conductor
of the consumer’s installation.
(5) In this regulation the expression “new connection” means the first electric line, or the
replacement of an existing electric line, to one or more consumer’s installations.
 
Surely with the regs stating unless designated circuit (cable more than 50mm in building fabric) or have skilled person permanently onsite etc then 99.9% of the time circuits should be protected by RCD, with a sky high zs the surely nuscience tripping is a problem, these rcds are mega sensitive, so there has to be some responsibility somewhere along the line for the earthing..... Its amazing the size and man power of these distributors but soon as you mention a earth system to them they shy away from it and leave it to a man with hammer and a rod!
Well its like this: there not LEGALLY obliged to provide an earth for a consumer but can disconnect if they find a consumer with no means of earthing whatsoever and (for whatever reason) wont comply with their demands that an adiquate earthing arrangement be provided..........
 
Actually, in TN systems, it's only circuits of special locations that require RCD protection, and some believe that even those don't require the whole circuit to be protected.
The biggest problem now with TT systems, is providing discrimination between RCDs in series, what with the reduction of disconnection times in the 17th edition.
 
Actually, in TN systems, it's only circuits of special locations that require RCD protection, and some believe that even those don't require the whole circuit to be protected.
The biggest problem now with TT systems, is providing discrimination between RCDs in series, what with the reduction of disconnection times in the 17th edition.
So that rule out a 100mA s type then spin?
 

Reply to TT systems??? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
162
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
2
Replies
18
Views
1K
  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
804

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top