B

bozobro0

Why is it that when the DNO provide an earth at the head they fit a cover over the terminals that you cant get off unless you remove the cutout and cut the seals.Why cant they provide an earth block at the side of the head if you not supposed to access their terminal.They have supplied alot of premises around here over the years with PME. Most are still on a TT system,and alot of them have damaged or non existent cable to the rods.:frown2:
 
I'm not chastising anyone but I will say that a neutral loop impedance reading of below 0.35 Ohms is not an indication that PME provisions are installed on the network, many TN-S systems will meet this value but won't have any multiple earthing installed!

It's a gamble that's not worth the risk to me, you're altering the means of earthing for a start which is notifiable under Document P so there now exists a record of your involvement, also backed up by any invoice issued.

Is it just me here or is everyone doing a quick neutral impedance test then forming their own PME?

I know what you are saying, you cant just go round making every installation PME but the neutral impedence test is a quick safety check to carry out on an installation that has a PME label fitted by the DNO to the cutout before you terminate your main earthing conductor.
 
I'm not chastising anyone but I will say that a neutral loop impedance reading of below 0.35 Ohms is not an indication that PME provisions are installed on the network, many TN-S systems will meet this value but won't have any multiple earthing installed!

It's a gamble that's not worth the risk to me, you're altering the means of earthing for a start which is notifiable under Document P so there now exists a record of your involvement, also backed up by any invoice issued.

Is it just me here or is everyone doing a quick neutral impedance test then forming their own PME?


They would be very foolish people if they did that!!!
 

Reply to TT to PME Head Earth Terminal in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
204
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top