I had UK power Networks round to test whether my TT earth could be changed to PME at my house which it is now. They told me all ok and get utility supplier meter engineer to connect up. Called utility company, they said we don't do that. Just get electrician in to connect it up. I pointed out that I belive it is illegal for us to touch supply head - silence on other end, but eventually again said we don't do it. Called DNO back and told them, they were not happy but said it's definitely down to supplier. Anyone else had this problem.
 
Usually always UKPN who have done it for me in the past, they are usually anything to do with the head, up grades and supplies

whereas the energy supply company only really deal with the meters

however i had a UKPN guy on a job i was working on a month or so ago tell me that basically do a l-n loop test on the incoming head, if its below .35ohms just pme it yourself!!!, from his lips!

He acknowledged that it was a nightmare for us to arrange it and a pain for them to come out and do it

i asked him about confirming the pme supply is availiable and hes said pretty much the w hole network is now PmE including most of the existing TNS supplies, as they now will not guarentee the sheath as a reliable earth any more

the only places that may be a problem are extreme rural locations

so there you have it, he also gave me a big pack of meter seals, top man :)
 
Nope not a ''Top Man'' at all, ....More like a complete and utter Plonker, ....and a Dangerous one at that!!

You go ahead and make your own DIY PME connections if you're really that daft enough. One things for sure, your so-called Top Man will deny any and all contact with you, if and when all goes ---- up and the **** hits the fan on one of your DIY PME connections.

To be honest Welchyboy1, i'm more than just a little surprised, at you actually listening to this idiot!!
 
Nope not a ''Top Man'' at all, ....More like a complete and utter Plonker, ....and a Dangerous one at that!!

You go ahead and make your own DIY PME connections if you're really that daft enough. One things for sure, your so-called Top Man will deny any and all contact with you, if and when all goes ---- up and the **** hits the fan on one of your DIY PME connections.

To be honest Welchyboy1, i'm more than just a little surprised, at you actually listening to this idiot!!

Most of the heads in my area will have a 'PME available' sticker on them...alternatively you can get confirmation from the DNO that PME is available at the property. With either means of confirmation I have no qualms at all about connecting it myself.
 
Nope not a ''Top Man'' at all, ....More like a complete and utter Plonker, ....and a Dangerous one at that!!

You go ahead and make your own DIY PME connections if you're really that daft enough. One things for sure, your so-called Top Man will deny any and all contact with you, if and when all goes ---- up and the **** hits the fan on one of your DIY PME connections.

To be honest Welchyboy1, i'm more than just a little surprised, at you actually listening to this idiot!!


Lol, 'topman' was for the meter seals TBH, i have yet to carry out any PME connections myself, just maybe a little surprised how blase he was about it, they are usually really ---- about anything like that

but from what he said the only confirmation they generally look for about the suitability of a potential connection is a loop reading
 
I had UK power Networks round to test whether my TT earth could be changed to PME at my house which it is now. They told me all ok and get utility supplier meter engineer to connect up. Called utility company, they said we don't do that. Just get electrician in to connect it up. I pointed out that I belive it is illegal for us to touch supply head - silence on other end, but eventually again said we don't do it. Called DNO back and told them, they were not happy but said it's definitely down to supplier. Anyone else had this problem.

SSE here comes round makes a measurement and if possible the head will have the knockouts done to access the earth connection on the side and the screwhead. They won't make the connection(s) though, you have to do it!
 
We don't in my mpan area, all earth loop impendence tester's taken off us (measurement down to dno) , under no circumstances are we to connect the earth, will knock out cutout ready for the sparks to connect.

Which on the vast majority of heads involves needing to remove the cover plate to access the terminal block, which is in turn screwed down with the screw protected by the fuse carrier, which in order to remove means cutting the seals that you've just zealously put on it and everyone claims to be so precious that only the DNO can do it!

Madness rules.
 
Actually SSE use heads where there are knockouts over the terminal screws and entries for the cable.
If PME is available they knock them out so that the electrician can make the connection without tampering with the head.
 
Actually SSE use heads where there are knockouts over the terminal screws and entries for the cable.
If PME is available they knock them out so that the electrician can make the connection without tampering with the head.

I hope they can suggest that to WPD, then!! I get the distinct impression that the DNO's method of the day is largely defined by what was the cheapest deal to re-stock the shelves in the stores that week. I must have seen at least three different specs of split-con "nah mate, that's standard now, that is" in the last six months alone - Alu / Cu, Cu / Cu and Cu / Steel.
 
Which on the vast majority of heads involves needing to remove the cover plate to access the terminal block, which is in turn screwed down with the screw protected by the fuse carrier, which in order to remove means cutting the seals that you've just zealously put on it and everyone claims to be so precious that only the DNO can do it!

Madness rules.

I am talking about new connections , their is provision to access the met on new cut outs, plus self connect meters etc, no reason to cut seals.
 
SSE will even connect your tails to a self connect meter around here if the tails are there ready!

As I understand it Rockingit DNOs will generally have at least three different brands of kit in use so as to reduce the impact should a product recall be issued on any of them. But to be mixing and matching cable sounds plain daft
 

Reply to TT to PME problem. in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

Ok so just done a quick test on mine. Megger mft on high gives 0.30 Robin 4120dl on 20ohm hives 0.22 Robin 4120 on 200ohm gives 0.28 Bearing in...
Replies
5
Views
653
I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top