Hi, when installing a consumer unit in domestic premises, I have been swopping out the main switch for an S type 100ma rcd. The reason I have been doing this is advice given in the on-site guide. PG 34 & 35. Dual RCD boards : Stating that there is insufficient fault protection of the single insulated conductors from the bottom of the main switch to the top of the rcd's.
I have come across a few installs recently (TT) that don't have a rcd main switch, I queried this with the Technical Helpline & they state I don't need one.
Does anyone else install a RCD main switch.

Cheers
 
For TT the OSG suggests an insulating gland and a 100mA time delay RCD main switch if a dual RCD board is used due to the single insulation on the internal tails to the RCDs. If an all RCBO board is used the time delay RCD can be omitted. For a standard domestic install, single pole RCBOs are fine.
 
For TT the OSG suggests an insulating gland and a 100mA time delay RCD main switch if a dual RCD board is used due to the single insulation on the internal tails to the RCDs. If an all RCBO board is used the time delay RCD can be omitted. For a standard domestic install, single pole RCBOs are fine.
What is a non standard domestic install:D
 
Fair enough.
I'd say it's just an isolation point and doesn't contain similar switch gear assembly's as a consumer unit would circuit breakers,fuses etc.
That's my take on it anyway.
Main switch in a CU, 60947-3. Main switch for one of those DNO things 60947-3.
 
If there's a risk of an internal non-protected factory cable link coming adrift within a CU and making the enclosure live then there has to be at least an equal risk of the meter tails escaping from the main incomer and causing the same problem ? So the only way to be sure of dealing with these scenarios safely is to have an external S type RCD, I'd happily fit that in an insulated enclosure. Although realistically with proper workmanship neither will ever happen- Ah therein may lie the problem ! :)
 
I suppose the basic question is "is a switched fuse" considered the same as a fuse board?
I would say yes as it has similar switch gear i.e. A fuse with outgoing circuit ,main switch isolation double pole.
I would say yes as it has similar switch gear assemblies i.e. A fuse protecting an outgoing circuit and a double pole isolation mains switch
 

Reply to the thread, titled "TT With Amd 3 boards" which is posted in UK Electrical Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top