Hi,
The current carrying capacity tables in the BS 7671 for twin and earth cables are only for buildings that have thermal insulation. I'm working on a commercial building, the inner walls do not have thermal insulation, what can i use for the current carrying capacity of the cables. The tables that i've seen (for T&E in BS7671) derates the cables too much. I hope to hear from you soon.
Rgs
 
The tables in BS7671 are not only for buildings with thermal insulation, they contain the applicable basic installation methods too.

Cable size calculations are the same regardless of type of installation.

The current carrying capacity tables should always be used as part of the proper calculations and not as a go-to reference for current carrying capacity. The actual current capacity of a cable can be more or less than that shown in the tables depending on the applicable rating factors
 
The tables in BS7671 are not only for buildings with thermal insulation, they contain the applicable basic installation methods too.

Cable size calculations are the same regardless of type of installation.

The current carrying capacity tables should always be used as part of the proper calculations and not as a go-to reference for current carrying capacity. The actual current capacity of a cable can be more or less than that shown in the tables depending on the applicable rating factors
Thanks for replying so fast davesparks. I am referring to Table 4D5, it's the only table in the regs for twin and earth. You'll see that apart from if you have the cables clipped direct, all the other columns refer to thermal insulated walls or ceiling. My cables will be run behind the walls.
 
Thanks for replying so fast davesparks. I am referring to Table 4D5, it's the only table in the regs for twin and earth. You'll see that apart from if you have the cables clipped direct, all the other columns refer to thermal insulated walls or ceiling. My cables will be run behind the walls.

Will they run behind the wall in trunking? Clipped direct? On perforated cable tray? Etc…

I think you can see where I’m going with this.
 
Thanks for replying so fast davesparks. I am referring to Table 4D5, it's the only table in the regs for twin and earth. You'll see that apart from if you have the cables clipped direct, all the other columns refer to thermal insulated walls or ceiling. My cables will be run behind the walls.

Which referenece method from table 4A2 are they going to be closest to?
 
Will they run behind the wall in trunking? Clipped direct? On perforated cable tray? Etc…

I think you can see where I’m going with this.
I imagine they'll run in the cavity and not in trunking or conduit or tray, probably clipped when i think about it. Can't quite remember how i've seen this done on site. Back in the day it was conduit in the walls probably to costly for that these days. They are circuits for wall sockets. I'm actually a electrical design consultant.
 
Will they run behind the wall in trunking? Clipped direct? On perforated cable tray? Etc…

I think you can see where I’m going with this.
I got it, so use reference method C. Can't believe i couldn't work that out before, thank you all for reigniting my brain cells.
Going to bed now. Night
 
I got it, so use reference method C. Can't believe i couldn't work that out before, thank you all for reigniting my brain cells.
Going to bed now. Night

No worries, glad you got there in the end. Sometimes we can’t see the wood for the trees, and need a little inspiration.
 
I wonder why you would be using T&E in a commercial installation. Usually I would be thinking singles in conduit surface mounted all the way through. Alternatively, dado trunking. Personally I hate T&E in commercial, very untidy and inelegant. With singles and conduit/dado trunking you can chop and change to re-fit sockets and lighting at will without going into the fabric of the building. Any fault finding is inestimably easier as is repair and additions. And then of course with T&E you get those situations of spaghetti in the ceilings flopped all over the place and additions add to that over the years. Not a very well designed method imho.
 
I wonder why you would be using T&E in a commercial installation. Usually I would be thinking singles in conduit surface mounted all the way through. Alternatively, dado trunking. Personally I hate T&E in commercial, very untidy and inelegant. With singles and conduit/dado trunking you can chop and change to re-fit sockets and lighting at will without going into the fabric of the building. Any fault finding is inestimably easier as is repair and additions. And then of course with T&E you get those situations of spaghetti in the ceilings flopped all over the place and additions add to that over the years. Not a very well designed method imho.
Thanks for sharing your thoughts. For lower cost which includes getting away with not using trunking for singles, i think these days a few of us are going over to T&E from time to time.
 
I wonder why you would be using T&E in a commercial installation. Usually I would be thinking singles in conduit surface mounted all the way through. Alternatively, dado trunking. Personally I hate T&E in commercial, very untidy and inelegant. With singles and conduit/dado trunking you can chop and change to re-fit sockets and lighting at will without going into the fabric of the building. Any fault finding is inestimably easier as is repair and additions. And then of course with T&E you get those situations of spaghetti in the ceilings flopped all over the place and additions add to that over the years. Not a very well designed method imho.
Very well said. T&E is a domestic cable and really isn't generally the right choice in a non-domestic setting.
 
I wonder why you would be using T&E in a commercial installation.

Why not? If T&E is suitable for the job why not use it?

Personally I hate T&E in commercial, very untidy and inelegant.

Surely that is a result of bad workmanship, not a problem caused by the cable itself?

I'm pretty sure a lot of us can produce a much neater and more elegant installation with T&E than some people manage to achieve with other wiring systems.
 
T&E is a general purpose cable, there is no rule or regulation limiting its use to domestic installations.
I was careful not to state that it was generally prohibited, but the generally much higher fault currents on a reduced csa cpc and issues of adequate mechanical protection need to be considered. Really it is intended for domestic type installations and much superior choices exist for non-domestic installations. Let's be honest and agree that generally T&E is simply selected for low cost (comparatively) to proper containment systems etc.
 

Reply to twin and earth cabling size for commercial buildings in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
393
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
978
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Thanks for the advice! Much appreciated
Replies
6
Views
846
  • Question
In the current book (18th, amendment 2) it is under regs 433.2 and 434.2 In most domestic situations the usual approach is the whole circuit is...
Replies
3
Views
669

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top