Waste time was a bit harsh but the money we save will eventually be lost to testing, where as if we used the same size CPC we would only need to test PEFC/Ze at origin like we do PSCC.
Testing is not just confirming the calculations you know...
[automerge]1591774290[/automerge]
I'm trying to find the k factor for AWG wire sizes just so I can compare our CPCs.
The k-factor is about the material (copper, aluminium, steel) and acceptable temperature rise (so typically a few small variariation based on PVC, XLPE, etc). The units might vary, but so long as you work things out in one consistent standard (e.g. mm2) and then convert back in to equivalent AWG it is fine.
Actually that is a very good reason why SWG and AWG as cable sizing are pants - they have no direct usable value for calculation or comparison of size!
[automerge]1591776985[/automerge]
As others have said, the size is purely down to regulations.
The CPC does not normally carry current so it only
has to be big enough for fault clearing, but the historical and regional approach to sizing that may have varied massively depending on the type of circuit protection device and the assumed skill levels of those designing / installing the circuits.
In the UK at least you always had to size the OCPD for the thinnest of cables on the circuit for normal overload protection, so immediately under fault conditions (which a current to the CPC is) you would be looking at rapid disconnection and so the I2t ought to be low enough for a reduced-size CPC. But you also have to consider the mechanical aspect of CPC strength, termination and corrosion, etc, which is (I think) the reason for various lower limits on CPC size that you see in the BS regs.
In other regions they may have had different rules on circuit OCPD selection, or less rigorous guidance for installed length, etc, that resulted in a mandate for the same CPC size to manage the fault-clearing safely.