First thing - you are using an outdated version of IEC60364-5-54 the latest is 2011 the one you have is 2002
Secondly, it is very clear it can be calculated; in later versions this is noted under 543.1.4 - 'where it is desired not to calculate using 543.1.2 (The adiabatic equation) then the cross sectional area may be determined in accordance with table 54.7'
(the reference is 543.1.3 in BS BTW)
In your older version the table is reference 54.3, so I assume the wording is slightly different perhaps 543.1.2 is another reference, or it is stated elsewhere - perhaps after the table.
The title of the table in the 2011 version is: Minimum cross-sectional area of protective conductors (where not calculated in accordance with 543.1.2)
If you have the standard, could you post the pages either side of this table?
Perhaps that is the issue... Here are the requested pages:
View: https://Upload the image directly to the thread.com/9lRlWAY
View: https://Upload the image directly to the thread.com/a/tMdmTSg
The numbers "skip" due to the copy being in both English and French.
I do not have any updated versions of my IEC documents. They get ridiculously expensive when ordering hundreds of standards. Wish they were free like NFPA-70.
[automerge]1591899145[/automerge]
Considering the UK as often led the world on electrical safety that seems a bizarre statement to make.
My opinion? The UK is the first in the world. Although with things like PME I'd say you guys are going backward, not forward.
Adopting MCBs and RCDs in the 80s and 90s was as much about cost and refresh cycles of installation than by standards, or would it be better if now nobody could do any electrical work unless they bought a new CU filled with AFDD? They are safer, so is the cost-benefit trade off of many homes not being repaired or upgraded better than allowing such technology to be adopted as it becomes affordable?
AFDDs aren't safer. They came about for the exact reason the US does not test or have any restrictions on R1+R2.
Many 3rd world countries (and the USA <cough>)do not test fully, or have such high standards of design, so are they better than the UK approach?
I'd say its highly lopsided, major superiority mixed in with major deficits. The NEC is highly conservative typically resulting in services, feeders and branch circuits which are loaded to less than half of their already conservative rating. NEMA and UL equipment tends to be more robust than IEC equipment. Lug burn ups are less common in the US. Protection of wire is much more strict.
On the other hand earth wires are about 1/10th the size of current carrying wires, no testing, no loop impedance, no disconnection time requirements, no real de-rating for insulation, limited RCD use, no sleaving, no finger isolation in open equipment, less arc flash mitigation...
The thing is the NEC is more ligation driven. Under sized earth wires aren't making themselves well known due to steel framed buildings dominating universally wired in metal conduit which in of itself is recognized as an "effective ground fault current path". But with more large scale wooden buildings (like apartments and nursing homes) and I can see it making itself known... as such code will either change Table 250.122 or require GFP/GFCIs on all feeders and branch circuits.
I am not going to lie- article 250 of the NEC for years has been a hurriance of debate, revision, and misguided electrical theory.