Just that 138/240Y exists
A while back several members expressed skepticism that such a system was in existence being that it is not common Europe.
Ah!
It is not my area, but I think the UK has mostly delta primary and star (Y) secondary, certainly for the LV final it will almost certainly be a star-connected transformer secondary.
Question though- isn't line and neutral such that it is impossible to melt the insulation no matter how high the L-N loop? My understanding is that a circuit breaker's bi-metal will cover and all over load conditions.
Melting is only a concern for line to earth faults with a reduced sized CPC.
It depends.
In (almost) all cases a circuit has to be protected against a fault (i.e. short) but for some cases it need not be protected against an overload.
For example, a fixed load like a shower, or a sub-min that has a limited load by virtue of the sum of breakers, may have an OCPD that will meet the cable's adiabatic limit in a fault but is not going to stop it melting on an overload.
However, for the majority of cases the OCPD is sized for cable protection so then you would be right, that no matter what the fault current level it would save the cable even if it did not meet the disconnection times expected for shock protection.
Question- does the UK have series combination ratings? An example would be a 22kaic main breaker and a 10kaic feeder breaker where both will "see" 22,000 amps during a fault. This is allowed on the idea that the manufacturer has tested both breakers such that a fault over 10,000amps will cause both breakers to trip instantaneously.
Again it depends, but generally as most MCB/MCCB used here are energy-limiting then you will see "cascading values" in technical data from the manufacturers on what the upstream PFC can be for a combination of devices.
Usually it is a MCB/RCBO that is the downstream device (typically for final circuits below 63A or so), and a MCCB or fuse that is the upstream device (typically the protection for a sub-main or board incomer). The results are not always what you might expect, as if the upstream let-through gets too high you end up limited by the small downstream device's rating.
As an example that just happens to be based on my current project, a 100A BS88 fuse feeding the Hager NBN series of MCB (15kA break limit), for 6A and 10A MCBs the cascaded PFC limit is the 15kA of the MCB, but for the 16A and above MCBs the limit is the 80kA of the fuse.
Why you might ask? Well if you look further down through the Hager data you will find the 6A & 10A have
total selectivity with that fuse, so basically they do
all of the fault current interrupting, but at 16A the MCB/fuse selectivity limit is 13.6kA thus by time you reach the MCB's PFC limit of 15kA the BS88 fuse is already blowing and limiting the peak fault current and so protecting the MCB from an explosive ending.