r1 and r2 on a radial? as far as I knowr1 and r2 are readings required for a RFC
Oh no pete! Don't confuse the OP even more, I thought we were getting somewhere there. [emoji38]
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss two radials on 16 a mcb in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
r1 and r2 on a radial? as far as I knowr1 and r2 are readings required for a RFC
Oh no pete! Don't confuse the OP even more, I thought we were getting somewhere there. [emoji38]
Why cant you carry out R1+R2 readings on a radial ? .... I can??What What??
Why cant you carry out R1+R2 readings on a radial ? .... I can??
....I am now with you Pete ! .... haha.The OP mentioned r1 + r2 did he mean R1+R2??
to clarify. each 16A MCB has 1 radial circuit consisting of 2 branches. ​
So OP:
Step 1 - locate the sockets / outlets on "both" branches.
Step 2 - I & T each branch
Step 3 - record the higher readings however if, for example 1 leg is short and has low IR and the other is long and has good IR I would be inclined to record both sets of readings on the schedule of inspections..... and add a note in the inspection comments section.
some guys just don't know their arse (r's ) from their elbows.At last, a straightforward answer to (an initially befuddled) question.
Truth is, I've come across many electricians who don't know exactly how best to test & record such a scenario, so let's not be too hard on the OP. And yes, electricians mixing up their r1 & R1 etc, gets me too!
some guys just don't know their arse (r's ) from their elbows.
you been on that peroxide again?:frown2::frown2::frown2: