Hi whilst inspecting a job I have come across two circuits supplied from two different phases how should I deal with this as its supplied from two different boards.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Two rings in one room in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
HI
You don't need to mark them the regulation is refering to fixed equipment and not socket outlets, at what point would you have two socket circuits dismantled at the same time? The sockets have the same nominal nominal voltage to earth of 230 volts. It is ambiguos and has been removed from AMD1. Just to clarify, you do not have to identify, with voltage labels ,sockets or note that they are fed from differing phases and therefore pose a 400 volt threat. You would label them normally stating there circuit and phase dsesignation but thats all.
As I said, the reg should refer to fixed equipment, as was it's intent and how it was expected to be perceived , however the actual reg was ambiguous, which is why we are removing it from the regs in AMD1 .GN1 will be updated accordingly.
"We" would be the IET
Yes this is in the draft for public comment. the regulation will also be changed from 514.10.1 to 514.8.1 and is on page 52/53 of the DPC.
Hang on, your post has vanished!