I understand why the increased use of type a rcds are recommended however there’s something I don’t understand. If these type a rcds aren’t tripping at 1x on a normal 50hz ac cycle or at x5 then surely they can’t be fit for purpose because they are not detecting a potentially critical fault. In my understanding an MFT simulates a fault at a specific leakage current in order to trip the rcd. Type ac rcds trip without failure most of the time. But carry out exactly the same test under the same conditions on a type a RCD it fails to interrupt the supply. Obviously there’s a type a test on the mft but why is it acceptable that they fail the ac test when the circumstances and requirement for them to trip under fault conditions on an ac circuit hasn’t changed?
 
If we need double pole protection in TT installations, then fuses can’t be used.
So we have to condemn all those BS 3036 and BS1361 fuse boxes.
What about the DNO fuse, or plug top fuses?

Wait, what about single pole light switches?
What does any of that have to do with circuits protected by RCDs ?
 
Hager will move the goal posts to suit themselves..
Before metal boards it was stipulated by the manufacturer that RCBOs must not be used on TT systems and now it’s suddenly all ok..
When Hager done their Amd3 roadshow I quizzed them on quite a few things but he couldn’t break out of script, kept repeating the same nonsense.
Even the regs are guilty of it, would appear they are in cahoots with each other.
Not sure I agree with a lot of that comment.

I really don’t see the issue with A typeRCBO’s. I’ve probably fitted at least 100 and all have tested out fine.
 
Had some unusual things when testing the last 2 type A RCBOs I stuck in, set test meter to type A RCD, and both tripped at 1/2 IΔn, replaced them with new ones from a different place and still the same. The readings were the same with outgoing conductors connected and disconnected. Testing them with the meter set to type AC RCD gave normal results. I have previously tested quite a few type A RCBOs without issue. Perhaps meter is faulty. :(
 
Getting the Same as you @freddo on the last two Split load Hager Boards fitted...Both have tripped at 1/2 on all RCD's and giving me well over 40ms (X5) on the last board. I'm using a Kewtech Tester (KT64DL) which I've had no problems with before? Spoke to both Kewtech and Hager about this and both party's seem blame each other?!?
 
@freddo Well Kewtech Tech told me they were trying to get info out of Hager in regards to what mA @ X5 is needed if its between 150mA - 250mA the Kewtech cant do it at the standard setting and Kewtech units are not Variable (unlike the meggers are)?! So was told to carry out X5 @ 100mA??!!?? Which could possibly damage the RCD?! So not sure what the point of that is as this would be putting 500mA through the device? But also reading up people have suggested carrying out 1/2 @ 500mA (Giving you 250mA) which I believe Hager are saying is the recommend value needed for there Type A Devices. (CD285U)
 

Reply to Type A RCDs Vs Type AC in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top