what is the answer to this question please?

A 16amp Type C CB used to protect a three phase reduced low voltage circuit is subject to a maximum Zs value of?

How do I work this out?
 
what is the answer to this question please?

A 16amp Type C CB used to protect a three phase reduced low voltage circuit is subject to a maximum Zs value of?

How do I work this out?

no calculations needed , just look up the value in max Ze tables in bs7671 for 16a type C
the value is the same for single & 3 phase.
 
Am i missing something! IE, OSG page 119 Type c 60898 16a max zs = 1.16 ohms, BS7671 page 56 Type c 16a 60898 max zs = 1.44 ohms.

The value in the onsite guide is 80% of the value given in BS7671, as it allows for changes in Ze etc. This is the value you should not exceed when designing and installing a circuit, hence why it is in the onsite guide!
The 100% value (1.44) is the absolute maximum value which would allow enough current to flow to trip the MCB/fuse etc. in the required timescale. i.e 0.4s
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
type C Circuit breaker
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
31
Unsolved
--

Advert

Thread statistics

Created
hsharp,
Last reply from
D Skelton,
Replies
31
Views
4,186

Advert

Back
Top