Uk power gave us these options | on ElectriciansForums

Discuss Uk power gave us these options in the UK Electrical Forum area at ElectriciansForums.net

Joined
Dec 24, 2016
Messages
404
Reaction score
82
Location
london
I advised client call UK power networks
Because they had a Ze of 500 ohms on a TN-S

This is what they said to client
“They advised that we contact an electrician to provide an independent local earth and RCD protection or a new PME service to provide satisfactory value of EFLI and test the internal wiring”

TT - I really don’t want to put an earth rod Through a drain pipe in London.

When they say upgrade to a PME will they will change service head to a TNCS?

I thought they need to maintain TN-s supplies?
 
I also thought DNOs had to maintain their earthing arrangements, but a recent post on here (possibly by SparkyChick?) said that some DNOs are washing their hands of tns due to many being in a poor condition. I do not know the legality of it though...
Wilko, I read it as the DNO providing PME rather than the electrician. I read it as a local sparks providing TT and RCDs as one option and PME to be done by the DNO as the other.

And Chris, I think a rod through a drain will get a great Ra....as long as the taps are left running at least!! Seriously though I would like to know what the legal situation is regarding the maintenance of their earth. Is there anything under ESQCR I wonder..
 
These are exactly the same options that Western Power gave me. Pay to have them provide PME/TNCS (WPD charge ÂŁ118.56+VAT if the head already has a PME terminal and ÂŁ147.26+VAT if they need to change the head) or install an earth rod and all the carp that entails.

The last time, they did at least send an engineer who carried out the same tests as I did and advised that I stick a bonding clamp on the lead sheath (it was on the outer steel armour - and was providing a bad connection), which I duly did and got a great Ze.
 
I retired from ENWL a few years back, and as a fault technician came across this problem fairly often. Their policy is that if they provide an earth they will maintain it free of charge. If we came across a high ze it usually involved a lead sheathed cable, and no you can't use a compression clamp on it, you have to use the coil type. If the ze was below 1.6 ohms we would down size the main fuse, between 1.6 and 20 ohms we would fit a temporary rcd, unless the cu had one fitted, above that it was disconnected. We would usually attend and repair the same day, or the next. Pme isn't always an option, there are still a lot of premises without bonding to gas, water etc.
 
ESQCR I wonder..
Yes Reg 25 gives a requirement to maintain existing earth. I argued this just today. Although DNO had attended and stated earth was adequate I did not think it was and quoted reg 25. Also I said if you decline to upgrade, I will not proceed with work in house, and will advise HSE of my findings. New upgraded earth put in the same day, today. Thanks for that DNO! All done very diplomatically of course.
 

Reply to Uk power gave us these options in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Did anybody take this on at all? Just curious.
Replies
1
Views
689

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top