I advised client call UK power networks
Because they had a Ze of 500 ohms on a TN-S
This is what they said to client
“They advised that we contact an electrician to provide an independent local earth and RCD protection or a new PME service to provide satisfactory value of EFLI and test the internal wiring”
TT - I really don’t want to put an earth rod Through a drain pipe in London.
When they say upgrade to a PME will they will change service head to a TNCS?
I thought they need to maintain TN-s supplies?