Hi all. I've done an install and carried out all tests except Ze. The site is a large electronics factory. The install is supplied from a sub board but the board supplies equipment required to be on 24/7. I've heard about contacting the DNO. Any advice would be appreciated. Thomas
 
You can contact the local DNO to your area and get the Ze by request.

And they can tell you anything they like! .8 and .35 values are little more than a target, they pretty much have carte-blanche to provide what they want as it's not actually stipulated anywhere in regulations, however the Zs values of BS7671 must be adhered to.

But if it's a private supply or a very local TX then it's going to be rock bottom - so you then have an issue of high PFC. If the place has a down-period or shift change during the day, you could always make arrangements to have a couple of minutes in which to disconnect the earth conductor in order to do the test, so long as there is no danger to users. Maybe. Needs risk assessing carefully!
 
Seems a bit over kill to try and shut down a large 24/7 electronic factory for a small install of a few circuits ( im guessing there) Take a Zdb at main board and PFC. Ask to see a recent EICR or PIR and have a look at the Ze if it was done. Just put down Zdb and move on.
 
Seems a bit over kill to try and shut down a large 24/7 electronic factory for a small install of a few circuits ( im guessing there) Take a Zdb at main board and PFC. Ask to see a recent EICR or PIR and have a look at the Ze if it was done. Just put down Zdb and move on.

Just re-read the OP, and yes, as it's a sub then Zdb and go home!
 
when ive contacted the dno in the past they allways give me the max value probably cant be bothered looking for the true reading happened twice to me now anyone else had similar

It's because they don't know, the people on the phones are clueless and they're just programed to say 0.8 ect.. on command like robots.
 
What! you mean the DNO dont have a room filled with dusty filling cabinets covered in cob webs, with a draw in each, all neatly compartmentalised, in alphabetical order for every installation within the whole of Great Britain. No, they cant be as disorganised as me, can they?
 
What! you mean the DNO dont have a room filled with dusty filling cabinets covered in cob webs, with a draw in each, all neatly compartmentalised, in alphabetical order for every installation within the whole of Great Britain. No, they cant be as disorganised as me, can they?

I know its impracticable and near enough impossible. But when you think about it, and what the DNO actually represent...they bloody well should have a database that size lol.

I love ringing the DNO. Not.
 
Hey just take a Zs reading at DB and note on cert that unable to isolate whole instalation at time of test, think its known as Zdb
I work in large commercial property all the time and i note it as zdb. you cant be shutting down a big office set up or the like of, just to certify some new lighting or power circuit.
 
DNOs are hopeless....mine decided to wait until the supply gave up before coming out to do a repair....despite the property lights in question flickering like some insane disco, motor speeds hitting the deck etc.
Got a right raving at down the phone, particularly as the resident is disabled....that got their attention....and a quick 180 in attitude...
 

Reply to Unable to measure Ze in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
344
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
882
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
953
Depending on the specific battery you (intend to) buy, you might be able to just do Monster alternator -> LiFePo4 battery. The BMS for the fancy...
Replies
5
Views
348

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top