I have had a similar situation and phoned NICEIC tech helpline about it.
Answer was test where you have been able to bond to and the point you should of bonded to. If the result is less than 0.05 ohms then this is fine but record the deviation of bonding points on your MWIC certificate
 
Try to explain to the owner that he just as well get it done now or its gunna to have to be done in 2 years when he sells it, Not the kinda thing you can say "I dont want it done"
 
I knew someone who got bullied into fitting a floury when there was no c.p.c in the lighting circuit.

Bad news, but it tends to be the younger guys who get knocked about imo.
 
so, following on from sjm's post, bond to locasl pipework and use a wander lead to the water stop tap and gas meter locations, measure resistance of the pipes. if under 0.05, then record as a deviation on the cert. best you can do in the circs.
 
is that your actual readings? if so then just put deviation on cert and note the readings as well.
 
If your really not happy, than write a letter stating the reg number and the reason why it couldn't be carried out than get customer to sign it.
 
its the grant work he's doing, it gets inspected by a plumber in a suit and if there isnt a 10mm at the stop tap and gas meter the job fails and the company have so many days to put it right.
 
I have had a similar situation and phoned NICEIC tech helpline about it.
Answer was test where you have been able to bond to and the point you should of bonded to. If the result is less than 0.05 ohms then this is fine but record the deviation of bonding points on your MWIC certificate


am i right in saying though, if you bond at point of entry to property, if gas meter etc is external, you are still infact complying with bs7671
 
You sure it's an RCD, and not an ELCB If the installations that old ?? Either way, that RCD has got to be Replaced, end of story!!!!

I don't want to sound pedantic here but I feel it's important to make a distinction between Voltage Operated Earth Leakage Circuit Breakers (VOELCB) and Current Operated Earth Leakage Circuit Breakers.

The current operated devices are actually what we now know as RCD's but were badged as ELCB's when they were first produced and as long as they pass the usual instrument/functional tests, are fine to remain in service.

The voltage operated (yellow test button and terminal labelled 'frame') need to be replaced.
 
Last edited:

Reply to Unable to upgrade/add main bonding? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
782
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
789
loz2754
L
I generally thought double stack boards were more for situations where a portrait design is better suited to the cupboard - you still generally...
Replies
4
Views
488

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top