Regulation 411.3.1.2 states ....
Main bonding conductors shall connect to the main earthing terminal extraneous conductive parts.
It then goes on to say...
'Metallic pipes entering the building having an insulating section at their point of entry need not be connected to the protective equipotential bonding'.
Lets say we have a water pipe coming into the house in the plastic blue pipe, from then on its metal. The above reg makes me believe this does not need Main bonding, is that correct?
The above reg does not suggest we test the water pipe to see if it extraneous. It just says we have to bond extraneous parts, then it says not to bond if they come in to the house in an insulating section.
If we do test the water pipe it is likely that it will test at 1 or 2 ohms to earth (probably as it is usually connected to earth somewhere within the premises). Does this reg still imply not to bond in this case when we can clearly see an insulating section at point of entry?
Main bonding conductors shall connect to the main earthing terminal extraneous conductive parts.
It then goes on to say...
'Metallic pipes entering the building having an insulating section at their point of entry need not be connected to the protective equipotential bonding'.
Lets say we have a water pipe coming into the house in the plastic blue pipe, from then on its metal. The above reg makes me believe this does not need Main bonding, is that correct?
The above reg does not suggest we test the water pipe to see if it extraneous. It just says we have to bond extraneous parts, then it says not to bond if they come in to the house in an insulating section.
If we do test the water pipe it is likely that it will test at 1 or 2 ohms to earth (probably as it is usually connected to earth somewhere within the premises). Does this reg still imply not to bond in this case when we can clearly see an insulating section at point of entry?