Regulation 411.3.1.2 states ....

Main bonding conductors shall connect to the main earthing terminal extraneous conductive parts.

It then goes on to say...

'Metallic pipes entering the building having an insulating section at their point of entry need not be connected to the protective equipotential bonding'.

Lets say we have a water pipe coming into the house in the plastic blue pipe, from then on its metal. The above reg makes me believe this does not need Main bonding, is that correct?

The above reg does not suggest we test the water pipe to see if it extraneous. It just says we have to bond extraneous parts, then it says not to bond if they come in to the house in an insulating section.

If we do test the water pipe it is likely that it will test at 1 or 2 ohms to earth (probably as it is usually connected to earth somewhere within the premises). Does this reg still imply not to bond in this case when we can clearly see an insulating section at point of entry?
 
As you have mentioned already, measure resistance to MET from metallic pipework. <22Kohms = bond.

Obviously make sure parellel patha are disconnected first.
It's almost impossible to eliminate parallel paths, if there's a combi for example the gas service will be mechanically joined to the water pipes. The test for extraneousness (I just made that word up) is generally unreliable and I prefer to combine it with a visual assessment of how likely a water pipe is to become extraneous when entirely within a building. Unless the building is steel framed the likelihood is minimal.
 
It's almost impossible to eliminate parallel paths, if there's a combi for example the gas service will be mechanically joined to the water pipes. The test for extraneousness (I just made that word up) is generally unreliable and I prefer to combine it with a visual assessment of how likely a water pipe is to become extraneous when entirely within a building. Unless the building is steel framed the likelihood is minimal.
Especially in a 32nd floor flat!!
 
It's almost impossible to eliminate parallel paths, if there's a combi for example the gas service will be mechanically joined to the water pipes. The test for extraneousness (I just made that word up) is generally unreliable and I prefer to combine it with a visual assessment of how likely a water pipe is to become extraneous when entirely within a building. Unless the building is steel framed the likelihood is minimal.

I had the on site plumber take a small section out right after the stop tap so i could test it which eliminated all parellel paths lol. Serched everywhere are there was no other extraneous parts. I thibk the reason i got 30KOhms was resistance through the wat or i would have had greater than 99MOhms
 
Ever since I started electrics back in 1961 bonding/equipotential cross bonding extraneous metal has been it seems a dark art. With a myriad of opinions on it most wrong. And an almost superstitious "...if it's metal bond it!.." approach. I think in this case it is simpler than we may overthink it is. One caution though, I have been in houses that start with plastic to copper. The copper wends its way through the property to the back bath and or kitchen but goes sub floor in cement so in such a case...??? It is only that there is not one rule fits all a careful survey needs to be done to be sure bonding is not needed as @wirepuller said "...a careful visual inspection..." is required.
 
And an almost superstitious
you can sing this when you thinking about it Vort.;)

[ElectriciansForums.net] Understanding the new regulation regarding Main Bonding.
 
It's almost impossible to eliminate parallel paths, if there's a combi for example the gas service will be mechanically joined to the water pipes. The test for extraneousness (I just made that word up) is generally unreliable and I prefer to combine it with a visual assessment of how likely a water pipe is to become extraneous when entirely within a building. Unless the building is steel framed the likelihood is minimal.

Loving Extraneousness!! That should definitely be a word lol
 
Some good posts!

I agree, it can be almost impossible to eliminate all parallel paths so an extraneousness test (pinched from @wirepuller :)) isn't going to be that reliable.

I think I'll have a chat with my assessor when he comes and see what he says. Until then, I'll flip a coin to see if I'm going to bond! o_O
 
I don't think it is so hard to determine.

Parallel paths via cpc's will be a low impedance back to MET. You therefore won't know if it was extraneous as you now can't sensibly prove it anymore without disconnecting too much stuff.

If pipework it is at earth potential via a cpc even though it was not extraneous in its own right, you won't do any harm by bonding it, you are just safeguarding if it is truly extraneous.

Most of the sparks at firm I work for don't understand the difference between earthing and bonding lol........let alone making a decision if they should to install it haha
 
I don’t think I’d like to be the one taking that photo - he seems a little miffed!
he has every right to be miffed, as Sitting Bull and the S0iux took all the credit for wiping out Custard and his blue bellies at Little Big Horn
 
Surely if there is an insulated incoming service pipe or even a 3 inch insulating piece between metal incoming and installation pipework then it's impossible for a potential to be introduced from outside the building ? And therefore bonding is not required in such circumstances ?
 
You can't earth plastic end of story. don't be a dick.
Do you earth isolated sections of any sort of pipe.... water/oil etc etc??
My answer is probably not, it's your call.
BUT BUT
I have 2 tests to ask
1 IS IT EXPOSED METAL( OF ANY KIND) THAT HAS THE POTENTIAL TO BECOME ALIVE??????
If yes then the answer must be to earth bond it
2 What would be your defense in the coroners court?

Remember the regs are designed to confuse sparkies by legal numpties.
 
I thought aslong as it exceeded 7.67k ohms it is not to be considered an extraneous conductive part.
no. the figure is 22K Ohms. 7.67K is the value of a L-E earth fault or leakage that would trip a 30mA RCD.
 

Reply to Understanding the new regulation regarding Main Bonding. in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K
  • Question
4-5 hours for 150? no chance, this is 2024, 150 for 2 hours maybe, that said an hour seems pretty quick, not sure he did the job right
2
Replies
23
Views
2K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top