Regulation 411.3.1.2 states ....

Main bonding conductors shall connect to the main earthing terminal extraneous conductive parts.

It then goes on to say...

'Metallic pipes entering the building having an insulating section at their point of entry need not be connected to the protective equipotential bonding'.

Lets say we have a water pipe coming into the house in the plastic blue pipe, from then on its metal. The above reg makes me believe this does not need Main bonding, is that correct?

The above reg does not suggest we test the water pipe to see if it extraneous. It just says we have to bond extraneous parts, then it says not to bond if they come in to the house in an insulating section.

If we do test the water pipe it is likely that it will test at 1 or 2 ohms to earth (probably as it is usually connected to earth somewhere within the premises). Does this reg still imply not to bond in this case when we can clearly see an insulating section at point of entry?
 
You can't earth plastic end of story. don't be a dick.
Do you earth isolated sections of any sort of pipe.... water/oil etc etc??
My answer is probably not, it's your call.
BUT BUT
I have 2 tests to ask
1 IS IT EXPOSED METAL( OF ANY KIND) THAT HAS THE POTENTIAL TO BECOME ALIVE??????
If yes then the answer must be to earth bond it
2 What would be your defense in the coroners court?

Remember the regs are designed to confuse sparkies by legal numpties.
Exposed metal that is likely to become live under fault conditions will be or should be earthed, that is a requirement for an exposed conductive part. That is nothing whatsoever to do with bonding.
 

Reply to Understanding the new regulation regarding Main Bonding. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
386
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
966
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K
  • Question
4-5 hours for 150? no chance, this is 2024, 150 for 2 hours maybe, that said an hour seems pretty quick, not sure he did the job right
2
Replies
23
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top