An Inspection was done on my Rental Flat , and UNSATISFACTORY report issued . There was only one C3 (4.4- Plastic Consumer Unit ) Is this correct to issue UNSATISFACTORY report based on one C3 ..... Confronted with Engineer , but he is not willing to change ... Where I should complain for this. Page 4,5,6 attached here. Do I have any ground to complaint.
 

Attachments

  • REPORT PAGES.pdf
    62.3 KB · Views: 93
An Inspection was done on my Rental Flat , and UNSATISFACTORY report issued . There was only one C3 (4.4- Plastic Consumer Unit ) Is this correct to issue UNSATISFACTORY report based on one C3 ..... Confronted with Engineer , but he is not willing to change ... Where I should complain for this. Page 4,5,6 attached here. Do I have any ground to complaint.
What was listed on Page 2 (part 7 - observations and recommendations).

On page 1 directly under the "Unsatisfactory" rating, it even says -

"* An unsatisfactory assessment indicates that dangerous (Code C1) and/or potentially dangerous (Code C2)
conditions have been identified."

If only the C3 you mention for a plastic consumer unit, then yes the report should have been issued as satisfactory. Only, C1, C2 or FI (Further information) should lead to an unsatisfactory report.

Having a combustible (plastic) consumer unit is not grounds for a C2 and unsatisfactory unless there is a sign of thermal damage or loose terminals, which do not appear to show on the certificate

If the Engineer is not willing to change their outcome then I would suggest getting that in writing from them, then the NICEIC would be the place that you could approach to raise a complaint as they appear to be an NICEIC approved contractor.
 
C3 means improvement recommended so this alone cannot result in an unsatisfactory report as it's only a recommendation.

What was listed on Page 2 (part 7 - observations and recommendations).

On page 1 directly under the "Unsatisfactory" rating, it even says -

"* An unsatisfactory assessment indicates that dangerous (Code C1) and/or potentially dangerous (Code C2)
conditions have been identified."

If only the C3 you mention for a plastic consumer unit, then yes the report should have been issued as satisfactory. Only, C1, C2 or FI (Further information) should lead to an unsatisfactory report.

Having a combustible (plastic) consumer unit is not grounds for a C2 and unsatisfactory unless there is a sign of thermal damage or loose terminals, which do not appear to show on the certificate

If the Engineer is not willing to change their outcome then I would suggest getting that in writing from them, then the NICEIC would be the place that you could approach to raise a complaint as they appear to be an NICEIC approved contractor.
Please see page 2 , Here he did mention one C2 -- Bathroom light not IP rated... Why this is not found in the Inspection schedule...is it normal ... Also On Page 2 he clearly ticked N/A for observation and recommendations..
 

Attachments

  • PAGE 2.pdf
    130.3 KB · Views: 51
An Inspection was done on my Rental Flat , and UNSATISFACTORY report issued . There was only one C3 (4.4- Plastic Consumer Unit ) Is this correct to issue UNSATISFACTORY report based on one C3 ..... Confronted with Engineer , but he is not willing to change ... Where I should complain for this. Page 4,5,6 attached here. Do I have any ground to complaint.
When was the plastic CU installed if it was before the new regulations came into force it'not retrospective, was the CU install compliant at the time of installation?
 
Last edited:
As a landlord you are responsible for the electrical installation in your property and should listen to appropriate advice about it. So one option would be to replace the CU with a non-combustible one, use the sign-off from the (qualified) installer to "cancel" the unsatisfactory EICR - and sleep at night.

But I'd probably use a different sparky to do the job.
 
If a plastic insulated consumer unit is a fail (unsatisfactory) then millions of rentals will fall into this category...
A C3 is merely a recommendation, it has little to no baring on the safety of the electrical installation.
 
Very few of those observations can get away with a N/A

Condition of Suppliers head, meter, etc should be a tick. Should only be N/A if it’s not actually there. (Such as suppliers isolator, which is a relatively new idea and not every property has one)

There are pages full of N/A.
would love to see the circuits form and see if it tally’s with the actual DB
 
As a landlord you are responsible for the electrical installation in your property and should listen to appropriate advice about it. So one option would be to replace the CU with a non-combustible one, use the sign-off from the (qualified) installer to "cancel" the unsatisfactory EICR - and sleep at night.

But I'd probably use a different sparky to do the job.
As a landlord they have a duty to abide by the law and the law does not require an undamaged non combustible CU to be changed.

I can't imagine most landlords have too much of a problem sleeping at night.
 
There are two aspects to this.
To cover your landlord duties, if there is only one C2 there for a non IP rated bathroom light then just get another sparks to change it (it's not an expensive job or expensive light), and as long as you have a document saying it's repaired you have done what you need to do in terms of meeting the requirements of the legislation. You are then sorted for 5 years.

But the other aspect is I'd be quite concerned the inspection hasn't even looked at the supplier earthing arrangements or intake. It might be the supply for the flat is in a common area he didn't have access to, but this should have been noted as an operational limitation if so. Is it possible to see the whole report with the property and contractor details blanked out?
 

Reply to UNSATIFACTORY EICR REPORT BASED ON C3 in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

This fella puts his face to it about halfway through, he has an opinion on the very subject.
Replies
42
Views
4K
Sockets will probably be ok on one, a little inconvenient in the event of a fault though, I'd probably like a 7th rcbo in. Wonder if hes linked...
Replies
93
Views
7K
suffolkspark
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top