.....using the higher values since I don't know the difference between resistive and reactive loads...

The higher value is the "apparent power" (reactive) which is what you will be drawing -- i.e. use that for your current calcs not the lower "true power" (resistive) value. You dont need to apply any power factor correction to the higher values (reactive) .......
 
So reactive and resistive are just the technical terms for apparent and true power. I understand now. Thanks Badged01.

Another question before I go and buy a bigger regulator:

If I invested in much bigger wire and replaced the connection between the breaker box and the restaurant (it varies in length between about 20 metres and 50 metres depending on the height of the river) would I actually need a voltage regulator in the first place? Does a voltage regulator actually increase the wattage available? Or, if there's not enough to start with, then it won't work anyway?

Thanks in advance.
 
So reactive and resistive are just the technical terms for apparent and true power.

Not quite but for what you are doing I think helps explains it in sort of laymans terms!

Does a voltage regulator actually increase the wattage available?

Nope, it does what it says on the time and regulates the voltage to supposedly give a steady voltage. It will not increase your power!
 
I'm confused. Why would the cable coming directly from the breaker box to the restaurant (with no regulator in between) then not provide enough power for the four fridges and other stuff when there is 220V reaching the restaurant according to my multimeter?

Would a bigger cable increase the wattage reaching the restaurant? I can buy and wire up proper big black power line cable the same as we use for the three phases and neutral lines from the main road (black plastic with big silver wires twisted together inside...the size of one we use is 35 locally if that helps although I don't know 35 of what...although looking at it the diameter of the silver wires twisted together could be 35 mm but looks more to me). Would this make any difference?
 

Reply to Unsteady Voltage Regulator in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
939
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Hello Ric2013, MJPD29 and westward 10. I have a multimeter that I tested the voltage with and before I open the socket up I use a plug in tester...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top