hi guys

hoping you could give me your thoughts,

i am pricing for a consumer unit change, its an old fuseboard with re-wireables.
it has 16mm meter tails, but it has a fairly new looking 100A main fuse.

its a small-ish house..... 2 ring mains, 2 lighting radials, a couple of sockets in the garage, and an immersion heater radial,

i was wondering whether or not i could just down-grade the main fuse to a 60A and keep the existing 16mm tails( no damage, or signs of overheating or burning)
or whether i have to leave the fuse at 100A and fit 25mm tails?

there's no electric shower or oven,

i would appreciate your advice

many thanks
 
as above^^^ it may say 100A on the outside, but be a 60A fuse on the inside. just leave the 16mm tails in, and the fuse is not your responsibility.
 
As #2 & #3 the 16mm tails were probably installed by the DNO along with the fuse, I would be more concerned that the earthing and bonding was correct for the supply characteristics
 
its the dno 100A fuse,
at the moment i am just going on the sticker on the outside, it was late in the evening when i looked at the job, and couldnt pull the fuse to check,

wouldnt it be against the regs to leave the 16mm tails with a 100A fuse?

i just dont want to get any come backs
 
its the dno 100A fuse,
at the moment i am just going on the sticker on the outside, it was late in the evening when i looked at the job, and couldnt pull the fuse to check,

wouldnt it be against the regs to leave the 16mm tails with a 100A fuse?

i just dont want to get any come backs

The OSG pictures assume you are working on a new build....

Do they have 3 electric showers, multiple cookers, a canabis factory in the loft..... The usage for a house is unlikely to rise about 35 amps so I'd leave them welll alone.
 
Hold onto your snips martin,
The requirement for 25mm tails are part of the PME supply regulations so if the supply is PME there is no getting away from that
 
The OSG pictures assume you are working on a new build....

Do they have 3 electric showers, multiple cookers, a canabis factory in the loft..... The usage for a house is unlikely to rise about 35 amps so I'd leave them welll alone.

so, basically, if it does turn out to be a 100A fuse in the holder, it would still be ok to leave the 16mm tails due to a low demand?
 
its a tns supply, the only upgrade to the earthing i have to do is the main earth, all the main earth and earth bonding at the moment is 10mm
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
upgrade meter tails, or downgrade main incoming fuse??
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
63
Unsolved
--

Advert

Thread statistics

Created
martinsayer81,
Last reply from
Engineer54,
Replies
63
Views
14,706

Advert

Back
Top