martinsayer81

hi guys

hoping you could give me your thoughts,

i am pricing for a consumer unit change, its an old fuseboard with re-wireables.
it has 16mm meter tails, but it has a fairly new looking 100A main fuse.

its a small-ish house..... 2 ring mains, 2 lighting radials, a couple of sockets in the garage, and an immersion heater radial,

i was wondering whether or not i could just down-grade the main fuse to a 60A and keep the existing 16mm tails( no damage, or signs of overheating or burning)
or whether i have to leave the fuse at 100A and fit 25mm tails?

there's no electric shower or oven,

i would appreciate your advice

many thanks
 
yeah i agree its a forum ,free speech,etc etc sparks helping other sparks out with varieties of knowledge but some guys are just arrogant ,
the type of guys that sit there self at lunch , that no one likes
 
murdoch needs more than a troll badge ,guys obviously got issues and comes on here looking to see what post he can annoyingly comment on ,
SADDO


For someone with only 52 post and no thanks I think you need to adapt your approach if you're to remain on this forum. Step over the line and the mods will throw you off.

- - - Updated - - -

murdoch needs a troll badge, you troublemaker you lol.

Troll badge - cool!
 
For someone with only 52 post and no thanks I think you need to adapt your approach if you're to remain on this forum. Step over the line and the mods will throw you off.

- - - Updated - - -



Troll badge - cool!
can i taunt him for a bit murdoch......i can 100% guarentee that he wont be back after a taste of my argumentative skills....lol...
 
You only NEED 25mm tails is if there is a 100A cut out fuse. Otherwise 16mm will be fine!! It may be prudent to realise that a 100A cut out fuse can only be provided when the Ze/Zs available is adequate to provide clearance times....

I have yet to see a typical standard to large domestic installation come anywhere near drawing a 100A or anything close to it!! Far too many here take more notice of a guidance drawing in the OSG, than using their training and commonsense!!
 

Reply to upgrade meter tails, or downgrade main incoming fuse?? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
270
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
763
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
765

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
483
  • Question
Yeh that’s my thinking. I have to supply the box so can order a bigger 3 phase option to give myself a bit more room
Replies
3
Views
838

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top