Sample Questions C&G 2392-10 Certificate in Fundamental Inspection & Testing - paper 2
( 1 ) The person who tests and signs the Electrical Installation Certificate for an Electrical Installation should be ?
A – The owner of the Installation ,
B – The Electrical Contractor who carried out the work ,
C – A representative of the Owner of the premises ,
D – A Competent person from an inspection and test company ,
( 2 ) Before commencing an initial inspection and test , the inspector should have a copy of the ?
A – Heath and Safety at Work Act ,
B – Electricity at Work regulations 1989 ,
C – Guidance Note 1 – Selection and Erection ,
D – Installation Specification ,
( 3 ) Which of the following information is “ Not “ required by the person carrying out the inspection and test ?
A – The prospective fault current at the origin of the installation ,
B – The external loop impedance ( Ze ) ,
C – information on the manufacturer of the electrical equipment used in the ,
D – the method used for fault protection ,
( 4 ) Which of the following should accompany the inspection and test ?
A – two copies of test results ,
B – copies of the inspection and test schedules ,
C – copies of minor works certificates ,
D – invoices for any remedial work carried out ,
( 5 ) Which of the following statement is false ?
A – Inspection & Testing may be done in an order decided by the test engineer ,
B – Installations must be inspected and tested on completion and also during erection ,
C – The purpose of the inspected is to verify equipment is correctly selected and erected in accordance with BS7671 ,
D – Precautions shall be taken to avoid damage to property during Inspection & Testing ,
( 6 ) Which one of the following does not need to be checked for compliance during the visual Inspection of an installation , ?
A – Presence of fire barriers ,
B – Correct connection of the supply authority’s fuse ,
C – Routing of cables in safe zone ,
D – Connection of single pole device in phase conductors’ only ,
( 7 ) A visual Inspection is necessary before testing to check whether ?
A – There is adequate access to switchgear ,
B – The Zs is within the maximum allowed ,
C – The polarity of switches’ and fuses are correct ,
D – The insulation resistance is acceptable ,
( 8 ) The top surface of a consumer unit should be protected from ingress of dust to a standard of ?
A – IP2X B – IP4X C – IP5X D – IP6X
( 9 ) During Inspection of a distribution board containing exposed conductive parts it should be verified that ?
A – The board is situated at least 2 meters above ground level ,
B – The board has a handle and the door is shut ,
C – The door can only be opened with a key or tool ,
D – The board has at least ingress protection to IP2X ,
( 10 ) When inspecting a conductor used for circuit protection it must be verified that the conductor is ,
A – Green or green and yellow throughout its length ,
B – green and yellow for at least 100mm at both ends ,
C – Marked with numerals at both ends ,
D – Green and yellow throughout its length ,
( 11 ) Which one of the following tests can only be carried out after supply is connected ,
A – Earth fault loop impedance ,
B – Insulation resistance ,
C – Polarity , D – Continuity of the protective conductors’ ,
( 12 ) The minimum test voltage that should be applied when testing the insulation resistance of a SELV circuit is , ?
A – 500v - dc B – 500v - ac C – 250v - dc D –250v - ac
( 13 ) Given the following numbered tests, select the sequence in which these tests should be conducted for a new installation : ?
1 , functional , 2 , insulation resistance , 3 , polarity , 4 , continuity of final ring conductors’ , 5 , continuity of protective conductors’
A – 1,3,4,5,2, B – 4,5,3,2,1, C – 5,4,2,3,1, D – 2,3,4,5,1,
( 14 ) Insulation resistance testers are designed to measure ?
A – High resistance using an ac voltage ,
B – Low resistance using an ac voltage ,
C – Low resistance using an dc voltage ,
D – High resistance using an dc voltage ,
( 15 ) An approved voltage tester can be used to ?
A – Establish whether a circuit conductor is live or not ,
B – Determine the effectiveness of a disconnection device ,
C – Measure the resistance of an earth continuity conductor ,
D – Carry out continuity tests ,
( 16 ) The purpose of the test button of residual current device is to check the ?
B – Continuity of the earthing conductor ,
C – Earth electrode resistance ,
D – Mechanical operation of the rcd ,
( 17 ) Statement 1, – A polarity test is carried out with a loop tester , Statement 2 , A polarity test can confirm correct connection of conductors within an Edison screw lamp
A – Statement 1 is true , Statement 2 is false ,
B – Both Statement are true ,
C – Statement 1, is false , Statement 2 is true ,
D – Both Statement are false ,
( 18 ) Which one of the following tests should be conducted to verify protection by electrical separation of ELV and LV circuits ?
A – Verification of protection by barriers or enclosures to minimum of IP5X
B – An insulation resistance test at 500v dc , between ELV and LV circuits ,
C – testing between conductors’ of each ELV circuit at 250v dc ,
D – An insulation resistance test between ELV and LV circuits at 250v dc
( 19 ) The schedule for an electrical installation should include the following ?
A – Date of completion
B – Recommended dates for future periodic testing ,
C – BS numbers of all equipment within the installation ,
D – The rating and type of protective devices ,
( 20 ) For circuits having a nominal voltage of 230v , the minimum insulation resistance required is ?
A – 5.0 MΩ B – 1.0MΩ C – 0.5MΩ D – 0.25MΩ
( 21 ) When an Electrical Installation Certificate is issued , any defects or Omissions must be ?
A – Made good
B – Identified
C – Noted on the certificate
D – Notified to the client
( 22 ) The maximum earth loop impedance to BS 7671 : 2008 for a circuit protected by a 20A BS-88 ( gG )
Fuse given a 5 second disconnection time is ?
A – 7.42 Ω B – 2.91 Ω C – 1.84 Ω D – 1.35 Ω
( 23 ) The maximum disconnection time allowed for a TN systems with a nominal voltage of 250v ac , to earth is ?
A – 0.2 seconds B – 0.4 seconds C – 1 seconds D – 5 seconds
( 24 ) What is the maximum earth fault loop impedance allowed when using a 32A Type C circuit breaker
Giving a disconnection time of 5seconds , the nominal voltage to earth ( Uo ) is 55V ,
A – 0.34 Ω B – 0.40 Ω C – 0.17 Ω D – 0.09 Ω
( 25 ) A insulation resistance test is carried out on a single-phase 230v circuit, the minimum acceptable reading and correct test voltage to BS 7671 : 2008 should be ?
A – 0.5 MΩ and 250v dc , B – 1.0 MΩ and 500v dc , C – 0.5 MΩ and 500v dc , D – 2.0 MΩ and 500v dc ,
( 26 ) A circuit has an external earth loop impedance Ze of 0.6 Ω , the maximum value of ( R1 + R2 ) to BS 7671 : 2008 , on a circuit protected by a Type B 32A circuit breaker giving a 0.4 seconds disconnection time will be ?
A – 1.44 Ω B – 2.04 Ω C – 0.84 Ω D – 0.24 Ω
( 27 ) Any faults or defects identified an initial verification should be ?
A – Made good immediately ,
B – Noted on the certificate before issuing it to the client ,
C – Noted on the certificate and arrange to complete repairs ,
D – Made good before issuing the certificate ,
( 28 ) The type of certificate is issued after installing an additional socket outlet within an existing installation would be a ?
A – Minor Certificate ,
B – Verification and Test Certificate ,
C – Installation Certificate ,
D – Periodic Test Certificate ,
( 29 ) Which of the following tests is carried out on a “ live “ circuits ,
A – Insulation resistance ,
B – Earth fault loop impedance ,
C – Continuity of final ring circuit conductors ,
D – Polarity by Continuity methods ,
( 30 ) End-to-end resistance checks would be carried out on a ,
A – Radial circuit ,
B – Lighting circuit ,
C – Ring final circuit ,
D – Fused connection unit ,
( 1 )- B ( 2 )- D ( 3 )- C ( 4 )- B ( 5 )- A ( 6 )- B ( 7 )- A ( 8 )- B ( 9 )- C ( 10 )- D ( 11)- A ( 11) - A ( 12 )- C ( 13 )- C
( 14 )- D ( 15 )- A ( 16 )- D ( 17 )- C ( 18 )- B ( 19 )- D ( 20 )- B ( 21 )- A ( 22 )- B ( 23 )- A ( 24 )- C ( 25 )- B ( 26 )- C ( 27 )- D ( 28 )- A ( 29 )- B ( 30 )- C
A – 0.34 Ω B – 0.40 Ω C – 0.17Ω ↔ ( regs : 41.6 ) ۝ D – 0.09 Ω
Ps , they is a very very small little red heron in here guess which one , the clock is ticking ? :)
CoP: 3[SUP]rd[/SUP]
-&-s. Test probes& Leads . “ Important“ p/45.
-&-s. The product standard for test probes &leads is [ BS-EN-61010-031 ]
-&-s. Test probes & leads for use in conjunctionwith a . Voltmeter . Multimeter . Electricians test lamp : Voltage indicator .
In addition to the requirements of [ BS-EN-61010-031 ] Safety requirements for electrical equipmentfor measurements . control . &laboratory use . test probes & leads should comply with the recommendations given in HSE . GN-38
Testinstruments :
Alltest instruments should be safe . the current safety standard is BS-EN-61010 : Safetyrequirements for electrical equipment for measuring . control . &laboratory use . All new equipment should comply with this . or an equivalentstandard . Equipment pre-dating this standard is not necessarily unsafe .
Upvote 0
question 27 is pony.. does not state type of circuit
Doesn't need to. In fact the question doesn't even need to qualify the earthing system, technically, the answer is the same in all cases.
Now question 6, that's pony.
According to that answer, you would not be able to bring an installation up to the current Regulations, unless it already comformed.
Upvote 0
Classes of Equipment .
CoP :
17[SUP]th[/SUP] Edition .
Definitions : p/25 Class 1 :Class 11 : Class 111 :
p/287 : BS-EN-61140 : 2002 . Protection against electric shock .Common aspects for installation & equipment . Part . 2
Class 1 . equipment . Equipment in which protection againstelectric shock does not rely on “ Basic Insulation Only “ but which includes means for the connection of exposed-conductive-partsto a protective conductor in the fixed wiring of the installation – BS-EN-61140 .
The safety earthing terminal of a Class 1 equipment . which is connected to the exposed-conductive-parts . is normally indicated by the symbol .
Safety earthing terminal of Class 1 equipment .
Symbol for safety earthing terminal
Exposed-conductive-parts . must be connected to the ( MET) of the electrical installation be means of the . circuit protective conductor. of the circuit supplying equipment . BS-7671:2011 Section – 411 .
In . addition it is essential that within the installationthere is . co-ordination between the characteristics of the relevant protectivedevice which affords fault protection & the Earth Fault LoopImpedance ( Ze ) of the circuit .
Upvote 0
Class II1 . Equipment. p/25
In which protection against shock relies on . supply at (SELV ) & in which voltages higher than those higher than of ( SELV ) arenot generated – BS-EN-61140 .
Construction forClass 111 equipment are less stringentthan for Classes 1 . & 11 . as protection against electric shock isprovided by a reduction in . supply voltage to . Extra-low . & by a high degree of separation fromhigher voltage circuits from Earth .
If Class 111 equipment is fitted with a flexible cord & a plug for connection tothe ( SELV ) supply source . the plugmust not be [ dimensionally ] compatiblewith those used for any other system in the same premises . & must not havea protective conductor contact - Regulation 414.4.3. refers .
CoP :
Class 111 equipment should bear the construction mark . & safety transformer symbol .
Upvote 0
when conducting a formal visual inspection on equipment used outdoor,it is important that the equipment has a suitable
Upvote 0