well, i would always use 6mm , method C, up to 9kW.
 
Not to cast aspersions on goodys clients but I'm guessing (know) to comply with fire/building regs (esp being given permission to turn a kitchen into a bedroom) a degree of insulation would be required
 
In the OP it states 230V. Using 230V it works out at 6.22 ÎŹ. Use that with 240V and you will get 38.5A.
Nobody has changed ohm’s law. Same resistance with a higher voltage gives higher current. Simple?

Ah yes of course simple, except for when I'm being an idiot. Thanks Tony.
 
Last edited by a moderator:
I'm not particularly concerned as i'm my own entity/business. People like the OP are only good for my business as his posts can be linked as can his website to his posts. It's not libellous if its true

Though as a profession, you should be. Once the standards are lowered there's no going back
 
fuzzy, if you bothered to read the OP's original post, you would see that he's not asking how to fit a shower, just airing his plan and seeing if others agree. there are qualified sparks out there who will say " you must use 10mm cable for a shower".
 
Sorry should have said, i'm having dinner with a very senior member of the Govt over Christmas and will show them threads like this to show that you have incompetent people being allowed to work by competent scheme providers
 
The Lib-Dems will dine with anyone that pays the required

We await with anticipation the forthcoming amendments to statute legislation.

 
Last edited by a moderator:
As if I'd have dinner with a Lib Dem

Seriously
That's a pity, as they may have more sympathy for you views. Remember, Part P came about as a result of Jenny Tonges' (Lib-Dem MP at the time) daughter being killed in an electrical accident. Jennys' private members bill proposed a full blown statutory system under one registration authority, similar to Gas Safe. However, amendments added by Labour and Conservative MPs who were lobbied hard by the NICEIC, ESC, Unite and other vested intrests resulted in the castrated system of Part P we have now.
 

Reply to Using a 8.5KW shower on a 6mm circuit. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
152
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
962
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
There are two reasons for a fuse/mcb they are: 1) fault conditions - which must exist always, and be capable of operating for all points on the...
Replies
4
Views
1K
Do you have an iPhone? If so you can take scans that “flatten” the image through some technical magic via the Notes app, these are auto saved as...
Replies
1
Views
204

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top