Can i add additional sockets off a cirvuit that uses 1mm cpc within a 2.5t&e cable please?
Or can i use it to feed a switch spur then 2 x sockets?
Or can i use it to feed a switch spur then 2 x sockets?
Thanks for response. Can you suggest the calculation i would need to satisfy this?Yes the ring final in my house is predominantly 1.0mm² cpcs and I have added to it. It needs to satisfy adabatic requirements but it should do unless protected by a BS3036 30A fuse.