Vehicle chraging point - Section 722 | on ElectriciansForums

Discuss Vehicle chraging point - Section 722 in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Joined
Mar 15, 2012
Messages
1,968
Reaction score
638
Location
North West
I've been looking at a job installing a vehicle charging point on a commercial premises. Earthing facility is PME, installation is 3 phase.

Now looking at 722.411.4.1, it says a PME earthing facility shall not be used.........except where i, ii or iii applies.

i states - A charging point forms part of a 3 phase installation that also supplies loads other than for electric charging and because of the characteristics of the load of the installation, the maximum voltage between the main earthing terminal of the installation and earth in the event of an open circuit fault in the PEN conductor is not likely to exceed 70v.

Now it gives a formula in Annex A722 to calculate first the maximum neutral current of the installation, which you can then use to either calculate the load balance to prove the above exception OR to use to calculate the maximum Ra value should you have to use an earth rod. Now I/L1 etc are all straight forward, but it has no multiply, plus or minus sign between 0.5(I/L2 + I/L3), same again after 0.866, so does that mean I just put the sum in the brackets to the end of 0.5 or do I multiply the sum from the brackets to the 0.5 or add the sum from the brackets to 0.5 etc?.

The formula A.722.1 is √[(I/L1 - 0.5(I/L2 + I/L3)][SUP]2 + [/SUP][0.866(I/L2 - I/L30)][SUP]2


[/SUP]Now I/L1 etc are all straight forward, but it has no multiply, plus or minus sign between 0.5(I/L2 + I/L3), same again after 0.866, so does that mean I just put the sum in the brackets to the end of 0.5 or do I multiply the sum from the brackets to the 0.5 or add the sum from the brackets to 0.5 etc?.

The earth rod would be a bit of a nightmare as the the socket is going onto the rear of a shop in a shopping center, with a tarmac car park behind.

Any help much appreciated...:crazy:
 
In the example

0.5(I/L2+ I/L3)

You always calculate whats within the brackets first and then multiply that by what is next to the brackets.

In the bigger formula with the square root, again you calculate whats within the () first, then calculate whats within the [], square each of the [] products and then add them together and then square root!

Clear as mud! :smiley2:

Taking it step by step:

√[(I/L1 - 0.5(I/L2 + I/L3)][SUP]2 + [/SUP][0.866(I/L2 - I/L30)]2

√[(I/L1 - 0.5(A)][SUP]2 + [/SUP][0.866(B)]2

√[(I/L1 - C][SUP]2 + [/SUP][D]2

√[(E][SUP]2 + [/SUP][D]2

√F
 
I have no clue on this but i am very maths Based

Im = is the rms maximum neutral current o a 3-phase installation (in Amperes), including that of the electric vehicle charging load and any other loads, determined in accordance with Regulation 311.1

Im = SQR ( { [IL1 - 0.5(IL2+IL3)]^2 } + { [0.866(IL2-IL3)]^2 } )

if you want to break it down then
A = 0.5(IL2+IL3)
B = (IL1 - A)^2

X = 0.866(IL2-IL3)
Y = X^2

Im = SQR (B + Y)

IL1 IL2 IL3 = are the RMS values of current (in amperes) in lines 1, 2 and 3, respectively, that were used when determining the value of Im



I dont know were these I/L1 .. I/L3 comes from
 
Last edited by a moderator:

Reply to Vehicle chraging point - Section 722 in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
450
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I was at my shed this morning, and something came to my mind about installing a charge point and taking payments for charging cars. I say “shed”...
Replies
0
Views
769
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top