srl-8

Hi guys,

i have changed a fuse board today in a outbuilding/large shed (it has a kitchen and shower and lounge etc.. a )

It is a TT system with earth rod.

My ZE reading was 187 ohms - now the regs state I am ok upto 200, so I assumed this was ok.

All the R1 + R2 and insulation resistance came back normal.

When I carried out the ZS tests, the reading were very high, for example:

Shower circuit on a 40a MCB - 2.6 omhs !
Kitchen Ring on a 32a mcb - 2.7 omhs !

same for lounge and bedroom rings.

I have checked to regs and these figures are over the maximum allowed.


Any advice ???
 
if your R1+R2 readings came back as satisfactory then that circuit impedance should be OK. Therefore you need to start looking at other factors relating to this issue i.e your Ze!! Are you earthing conductors connected correctly and secure and in good condition?

Get another rod sank in and see if this is any better to lower your Ze
 
ZE was 187

the system is protected by a 30ma RCD from the main house, and the new board is also protected by a 30 ma RCD.

??


Ok then your maximum allowed Zs reading for each 30mA protected circuit is 1667 Ohms, problem solved in 31 posts.

Your RCD at the supply end should ideally be an 'S' type time delayed to achieve discrimination with the RCD at the remote end but I wouldn't loose sleep over that one.
 
ZE reading 187ohm

I can determine ZS by enquiry, ZE +R1 +R2 = ZS

However, i tried to test and measure ZS at the end of the circuit and got these high figures of 2.6 2.5 etc etc...

again, any ideas on how to solve this issue???

Thanks

ok, first it's not an issue.

When you tested Ze, You disconnected the earthing conductor which went to the earth rod I imagine.

As previosuly mentioned, you may well have bonding in place to the Water service???

Try testing with the earthing conductor re-connected, and you will probibly get a reading of somewhere around 2 ohms. As previsouly stated by telerix, by connecting the water pipe you've effectivly got a much better earth rod!

With regards to the values in the Regs - Being a TT system, because your Ze is not garenteed stable, circuits must be protected via RCD (in your case 30ma), which from what you say they already are.
 
Last edited by a moderator:
ZE was 187

the system is protected by a 30ma RCD from the main house, and the new board is also protected by a 30 ma RCD.

would that be a 30mA RCD protecting the sub main and another 30mA RCD protecting the final circuits in the outbuilding i.e. 2 RCD's in series

I was too slow in replying to specialist (too slow, specialist beat me) sorry to cause confusion
 
Last edited:
I'm busy writing an FAQ on TT systems for a certain organisation, judging by some of the questions (and answers) on this thread, I need to write faster!
 
ZE was 187

the system is protected by a 30ma RCD from the main house, and the new board is also protected by a 30 ma RCD.

would that be a 30mA RCD protecting the sub main and another 30mA RCD protecting the final circuits in the outbuilding i.e. 2 RCD's in series

too slow, specialist beat me

Hey: I've got to beat someone at posting at least once a year:lol:
 
sorry if i read that wrong mechelec but why would 2 rcd`s in series slow the disconnection time

It wouldn't, in practice, both devices would trip under fault conditions because there would be no discrimination without the upstream device being an 'S' type time delayed.
 

Reply to Very Hi ZS Reading on TT system? any advice in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
594
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
949

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
792
S
  • Article
Unidentified noise in party wall Hi 🙂 Please can anyone help to identify this noise in the wall between me and my neighbour? Complicated but will...
Replies
0
Views
232
shrewmouse
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top