Hi guys,

i have changed a fuse board today in a outbuilding/large shed (it has a kitchen and shower and lounge etc.. a )

It is a TT system with earth rod.

My ZE reading was 187 ohms - now the regs state I am ok upto 200, so I assumed this was ok.

All the R1 + R2 and insulation resistance came back normal.

When I carried out the ZS tests, the reading were very high, for example:

Shower circuit on a 40a MCB - 2.6 omhs !
Kitchen Ring on a 32a mcb - 2.7 omhs !

same for lounge and bedroom rings.

I have checked to regs and these figures are over the maximum allowed.


Any advice ???
 
sorry if i read that wrong mechelec but why would 2 rcd`s in series slow the disconnection time

It wouldn't "slow the discrimination time? " but it would mean there was no discrimination between the RCD's and it would be pot luck which would trip first. inconvenient at best, dangerous at its worst. First one should be time delayed or S type
 
So to confirm,

ZS readings of 2.6 ohms or there abouts is acceptable, providing the system and all circuits are protected by a 30ma RCD. (which they are)

??


Ok then your maximum allowed Zs reading for each 30mA protected circuit is 1667 Ohms, problem solved in 31 posts.

Your RCD at the supply end should ideally be an 'S' type time delayed to achieve discrimination with the RCD at the remote end but I wouldn't loose sleep over that one.
 
i got confused earlier, because a member said the my ZS reading could never be lower than my ZE...

My ZS of 2.6 etc is lower than 187 omhs.....?

So to confirm,

ZS readings of 2.6 ohms or there abouts is acceptable, providing the system and all circuits are protected by a 30ma RCD. (which they are)

??
 
It wouldn't "slow the discrimination time? " but it would mean there was no discrimination between the RCD's and it would be pot luck which would trip first. inconvenient at best, dangerous at its worst. First one should be time delayed or S type
yeah well this one cropped up here a while back......2 RCDs..both 30mA...both in series...one feeds the house..the other the garage/outbuilding...theres a fault in the garage/outbuilding...which lets go first?...
 
Last edited by a moderator:
i got confused earlier, because a member said the my ZS reading could never be lower than my ZE...

My ZS of 2.6 etc is lower than 187 omhs.....?

It's often lower because of parallel paths from bonding conductors etc. I explained in post 4.

Your 187 Ohms is Ra NOT Ze on a TT system, this is all in the On-Site Guide that you already mentioned, PLEASE read it thoroughly, there are large gaps in your knowledge and someone could be hurt because of this!
 
It's often lower because of parallel paths from bonding conductors etc. I explained in post 4.

Your 187 Ohms is Ra NOT Ze on a TT system, this is all in the On-Site Guide that you already mentioned, PLEASE read it thoroughly, there are large gaps in your knowledge and someone could be hurt because of this!

In mine too nowadays which I'm blaming on Alzheimer's. :(
 
You're scaring me Eng54. :aureola: This isn't some kinda new years resolution is it?


Not really, just that there are more than enough posters on this thread already!! lol!!

Does seem strange though, that the OP is more than satisfied with his Ra of 185 ohms or whatever, ...and for his own house!! Seems he didn't even give a thought to adding a couple of rods at the workshop end, or adding on a rod, at the existing rod for the house.... Oh well, his house and his family!!! lol!!!
 
Not really, just that there are more than enough posters on this thread already!! lol!!

Does seem strange though, that the OP is more than satisfied with his Ra of 185 ohms or whatever, ...and for his own house!! Seems he didn't even give a thought to adding a couple of rods at the workshop end, or adding on a rod, at the existing rod for the house.... Oh well, his house and his family!!! lol!!!
how about a lovely gas pipe..lol....
 
just to confirm, I never said I was satified with my high RA, just giving the facts and hope to get good information from the forum.

I will be looking to lower the RA, however it is deemed as ok according to the Regs..


Not really, just that there are more than enough posters on this thread already!! lol!!

Does seem strange though, that the OP is more than satisfied with his Ra of 185 ohms or whatever, ...and for his own house!! Seems he didn't even give a thought to adding a couple of rods at the workshop end, or adding on a rod, at the existing rod for the house.... Oh well, his house and his family!!! lol!!!
 

Reply to Very Hi ZS Reading on TT system? any advice in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
594
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
949

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
792
S
  • Article
Unidentified noise in party wall Hi 🙂 Please can anyone help to identify this noise in the wall between me and my neighbour? Complicated but will...
Replies
0
Views
232
shrewmouse
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top