C

chloebear

Hi All,

Just been testing out some existing ring circuits in an existing building and I am when checking out Rn & R1 on the ring circuits all seems Ok with readings between 0.89 & 1.12 for 2.5mm singles, but when checking the cpc I am getting very low readings of between 0.01 & 0.03 for the same circuits as above????????? The majority of the installation is in steel conduit & box trunking, but as far as I can see the conduit system has not been used as the cpc.

Any thoughts??????????????????????????
 
......and a knowledge of the type of installation to be tested/inspected.

Key words when undertaking periodic inspections.
 
Bit late to join the party, but you did test the right CPC's ? Very easy if a dedicated CPC is installed for someone before you to not connect in the same sequence of the earth bar as you think, and if you have several circuits coming into the board via one conduit it is easily done.

I would make 100% sure you have the right 2 CPCs for the ring final.
 
Seeing as the last reply to this thread was in 2011 I think it is safe to say the op will have resolved any problems he had, Thread closed.
 

Reply to Very low CPC Readings in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
275
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
773
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
779

Similar threads

I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top