chloebear

Hi All,

Just been testing out some existing ring circuits in an existing building and I am when checking out Rn & R1 on the ring circuits all seems Ok with readings between 0.89 & 1.12 for 2.5mm singles, but when checking the cpc I am getting very low readings of between 0.01 & 0.03 for the same circuits as above????????? The majority of the installation is in steel conduit & box trunking, but as far as I can see the conduit system has not been used as the cpc.

Any thoughts??????????????????????????
 
......and a knowledge of the type of installation to be tested/inspected.

Key words when undertaking periodic inspections.
 
Bit late to join the party, but you did test the right CPC's ? Very easy if a dedicated CPC is installed for someone before you to not connect in the same sequence of the earth bar as you think, and if you have several circuits coming into the board via one conduit it is easily done.

I would make 100% sure you have the right 2 CPCs for the ring final.
 
if its in conduit you are also have fly leads on lighting circuits and other rings or radial circuits are you going to dissconect all of them as well because you will be on about 2p an hour
 

Reply to the thread, titled "Very low CPC Readings" which is posted in Australia on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top