Volt drop cable calculator | Page 2 | on ElectriciansForums
Discuss Volt drop cable calculator in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Learn it as "milliVolts per amp per metre" rather than "em-vee ay-em" and it will make more sense. Div by 1000 because you want the anwer in Volts, not milliVolts.
Where does this "Factor(1.20)" come from, moose?
the 1.2 factor is to allow for resistance variation with temperature. the tabled values are at 20dg.C so the actual figure at operating temp. will be higher.
The values in the tables are for the cables running at their maximum operating temperature.
You don't need this 1.2 factor for Volt drop calcs.
You can reduce the voltage drop for cables operating at lower temps by using the equation in App 4, 6.1
i stand corrected. was thinking of th resistance tables. you are correct in saying that the tabled values are @70deg.
Reply to Volt drop cable calculator in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
The cable is way undersized. If the voltage drop is detrimental to the installation I would make a mention of it as volt drop generally is not...
I created a voltage drop spreadsheet for this sort of thing. I used to use it to calculate the drop when designing regular 230V lighting circuits...