How does a FCU differ to a 1 way CU? Both have DP isolation, both have an OPD and max Zs values of BS1362 fuses are printed in BS7671 so why can't we add a separate schedule of test results for the outgoing side of a FCU?
DB reference - FCU/1
Location - Kitchen
Zs at DB - 0.38ohms
Ipf - 0.61kA
blah blah blah!
If the maximum Zs of the load side of the FCU is less than that allowed by a B32 MCB then you may not need to go to that length but if it ends up being higher due to the length of the circuit then by treating the load side individually you can show that the max measured (or calculated) Zs is within limits for the chosen BS1362 fuse.
Just thinking out of the box