Can you up the cable size to 4mm for the spur from the RFC? Assuming you're calculating it at 2.5mm ATM.Yes. The garden sockets will be protected by the RFC RCD at source.
Ah, OK. I thought you were having a VDrop issue because of the planned length of that part of the circuit.Err no. The customer has already had the builders install 2.5mm SWA under the new patio. Its been left for connection. I don't have too many worries about the VD or ZS but it just started me thinking about ZS and VD TBH. I
Pedantic I know...!
BS1362 fuse.
Zs @ 0.4s, 3A = 16.4, 13A = 2.42 ohms.
Where are those figures from Archy?
if you look on the page beofre mate, they are there at the bottom.Found them here...
http://www.shepleyelectricalservices.com/Max%20ZS%20Table.pdf
BRB only gives 5sec Z esses for 1362s.
Look upon the supply to the FCU as a distribution circuit with protection from a B32A MCB and the final circuit from the FCU with protection from a BS1362 fuse.
You could add a second schedule of test results just for the final circuit from the FCU, treating the FCU as a distribution point.
Volt drop is measured from the origin of the installation.