I am going to be installing a sub main from a house db (at meter position) to shed(1), then from that shed to shed(2), then from that to shed(3).
I am aware that lighting is max 3% drop (6.9v of 230v)
non lighting is max 5% drop (11.5v of 230v)
voltage under no load at supply is 240v. To comply with regs do i disregard this and work on basis of 230v?
In sheds there are only going to be 13a sockets
But sub mains will vary in length and cable size.
So does this mean that i can lose max of 11.5v to the shed 3 socket outlet from meter (house db) ?
Would i go about it like this: , 230v at origin, 1st submain is say 5v loss,
then for the second submain: calculate the next volt drop from 225v?
and then just ensure that through calculation no more than 11.5v has been lost at the furthest point of furthest
circuit, ie a socket outlet of shed 3?
Also what would the ambient temperature typically be if the swa cable is installed 2 feet underground.
thank you.
I am aware that lighting is max 3% drop (6.9v of 230v)
non lighting is max 5% drop (11.5v of 230v)
voltage under no load at supply is 240v. To comply with regs do i disregard this and work on basis of 230v?
In sheds there are only going to be 13a sockets
But sub mains will vary in length and cable size.
So does this mean that i can lose max of 11.5v to the shed 3 socket outlet from meter (house db) ?
Would i go about it like this: , 230v at origin, 1st submain is say 5v loss,
then for the second submain: calculate the next volt drop from 225v?
and then just ensure that through calculation no more than 11.5v has been lost at the furthest point of furthest
circuit, ie a socket outlet of shed 3?
Also what would the ambient temperature typically be if the swa cable is installed 2 feet underground.
thank you.