Hi All,

I am at my wits end here so here goes...

On Monday I was called to a domestic premises with reported shocks occuring while the client was taking a shower. This was apparently first noticed over 2 weeks ago!

We proceeded to do all the relevant checks on Earth Bonding and various testing including IR on all circuits. Most circuits proved to be fine apart from a high Zs (3.06) on the upstairs ring. All bonding was proved to be sound. Install is a PME with a split board with only 1 RCD. Main incomer has a Zs of 0.26. I moved all circuits over to RCD protection to see if any tripping would occur....to no avail.

Upon further investigation we ran a lead out from the board to provide a means of testing in the shower...what is clear is that a voltage of 6v can be meaured between Earth and the actual water in the shower tray but ONLY WHEN IT IS DRAINING THROUGH THE WASTE! This voltage increases to around 18v at least as load is increased around the house.

Upon FURTHER investigation I have now discovered this to be the case on all 3 showers and all basins upstairs. With the basins I actually filled them up, released the plug then could measure the voltage as the water drained...NOT BEFORE. With the showers I ran the water and turned off then measured the voltage again as the water drained. All showers are hot and cold fed with no local pumps.

I have had every circuit apart and individually connected 1 circuit at a time in the board and found that 4 out of the 6 circuits seemed to bring about the voltage. I have also bizarrely placed a lead between the mixer taps and into the water in the plug hole while running the water. This always removes the voltage.

I am left with the only answer that somehow a voltage is finding its way through the waste water and once someone gives it a path then the shock occurs!!

I have had SSE out today checking everything their end....no problems. Contacted the NICEIC...no advice could be given! I've consulted 2 of my so called guru electricians who are stumped. I am hoping that tomorrows investigation of the external wiring will reveal something but I'm not holding my breath!

Somebody please tell me they have come accross this before!!
 
I have not read the full thread, so i may be on the wrong track here, but you never know.

Is all the supplementary bonding in place where is should be? Irrespective of whether or not BS7671 says it should or doesnt have to be.

I have never had this fault, but i have had my fair share of head scratchers, and when i have eventually got to the bottom of it, the problem was usually staring me in the face. I am not trying to imply that you have overlooked anything, but i thought it worth a mention, we are all human, and frustration can fog the issue at times.

Cheers..........Howard
 
As the DNO have been, the seals will undoubtedly have fallen off the bullet and the main fuse has fallen out. This is a good thing as it means you can test to see whether you still have a voltage present with the installation 'dead' but the neutral still in place, something you can't do using the DP main switch. If you DO still have a voltage present then it's back-feed from somewhere outside of your installation, if you don't then it has to be yours, and start with everything off at the board then turn it all back on a circuit at a time until your problem appears.
 
Umm, did anybody notice those IR readings in post #55:

The following IR readings were taken with each circuit completely disconnected on 500v - 20mohm. I literally had a lead poked into the waste with he water running.

Live to water
Lights Down - 0.62
Lights Up - Clear
Skts Down - 3.07
Skts Up - 0.63
Smokes - Clear
Cooker - 13.55

Earth to water
Lights Down - 0.45
Lights Up - 0.3
Skts Down - 0.07
Skts Up - 0.07
Smokes - Clear
Cooker - 0.08

Water to Met - 0.07
Water to Neutral Bar - 2.45
Water to Bond - 0.08

Now 620kΩ from line won't kill you and won't trip an RCD, and I'm not sure it's the direct cause of the shocks, but it's unusually low and a failure anyway. The fact that two unrelated circuits are coming in with similar low insulation is rather striking. Upstairs sockets and downstairs lights both have a tale to tell, I think.
 
Umm, did anybody notice those IR readings in post #55:



Now 620kΩ from line won't kill you and won't trip an RCD, and I'm not sure it's the direct cause of the shocks, but it's unusually low and a failure anyway. The fact that two unrelated circuits are coming in with similar low insulation is rather striking. Upstairs sockets and downstairs lights both have a tale to tell, I think.

I looked at those and they scream that something is very very not quite right about this whole affair. It's PME, right? So, the Neutral and MET are effectively one and the same, agreed? So, how come there's 2M difference in a reading? (assumes no RCD in cct). And if we're now looking at lights AND sockets....exactly how many screws do we think have pierced these three pipes which magically stop conducting before they all join together??

If this is a genuine thread, then I think maybe a fresh pair of eyes may be needed on the job.
 
If suspect circuits are downstairs lighting and upstairs sockets, it seems fair to assume that at least some of the cabling shares a common route.

Could it be possible that nail or screw damage has occurred in one place to the cables and a waste pipe, causing a small water leak which not only is causing voltage to appear on that waste, but the water leak is also tracking down the outside of pipe to the external discharge point where it comes into contact with the waste water from other two pipes, thus causing voltage to appear in those too.

May not even be nail or screw penetration to cables or pipe. Could just be a combination of cable damage (rodents?) with a poorly connected and leaking waste from shower, basin, etc. This is tracking on outside of waste pipe as above.

Just thinking out loud. May be way off the mark with this thought process.
 
OP - what is your background / experience / testing knowledge?
 
Hi, I'm Mark, the homeowner, just wanted to say thank you to all of you for your time here and input and of course to my sparky. Really humbled and grateful for helping us sort the problem. If any of you want to hook up via Google+/Skype video so I can show you around the house (if this is of any use), I happy to do that.
 
How thoroughly checked have you for polarity reversal?
 

Reply to Voltage in shower waste! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
317
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
964

Similar threads

  • Question
I went to look at a job like this a few years ago. My customer had a rental house, where there was an upstairs bedroom that had a newly built stud...
    • Informative
    • Like
2
Replies
15
Views
3K
Question 1 do you prefer buttered, salted or sweet salted? I'm guessing salty 😜 1. Auto range multimeter (used on mains before when testing the...
Replies
2
Views
616

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top