Hi All,

I am at my wits end here so here goes...

On Monday I was called to a domestic premises with reported shocks occuring while the client was taking a shower. This was apparently first noticed over 2 weeks ago!

We proceeded to do all the relevant checks on Earth Bonding and various testing including IR on all circuits. Most circuits proved to be fine apart from a high Zs (3.06) on the upstairs ring. All bonding was proved to be sound. Install is a PME with a split board with only 1 RCD. Main incomer has a Zs of 0.26. I moved all circuits over to RCD protection to see if any tripping would occur....to no avail.

Upon further investigation we ran a lead out from the board to provide a means of testing in the shower...what is clear is that a voltage of 6v can be meaured between Earth and the actual water in the shower tray but ONLY WHEN IT IS DRAINING THROUGH THE WASTE! This voltage increases to around 18v at least as load is increased around the house.

Upon FURTHER investigation I have now discovered this to be the case on all 3 showers and all basins upstairs. With the basins I actually filled them up, released the plug then could measure the voltage as the water drained...NOT BEFORE. With the showers I ran the water and turned off then measured the voltage again as the water drained. All showers are hot and cold fed with no local pumps.

I have had every circuit apart and individually connected 1 circuit at a time in the board and found that 4 out of the 6 circuits seemed to bring about the voltage. I have also bizarrely placed a lead between the mixer taps and into the water in the plug hole while running the water. This always removes the voltage.

I am left with the only answer that somehow a voltage is finding its way through the waste water and once someone gives it a path then the shock occurs!!

I have had SSE out today checking everything their end....no problems. Contacted the NICEIC...no advice could be given! I've consulted 2 of my so called guru electricians who are stumped. I am hoping that tomorrows investigation of the external wiring will reveal something but I'm not holding my breath!

Somebody please tell me they have come accross this before!!
 
Lol sorry people! I've not abandoned you honest! Just getting as much info as pos. If you've not seen yet then I'll enlighten you.

Today I found 25v on the metal studwork in 2 seperate places oon the 1st floor. Appeared to be directly energized by the lighting circuit. However once the lighting circuit was completely removed the other circuits combined brought back 7v. Af least now I have metal to test to instead of water! To experiment I put a bond to the metal work in one room which removed the 7v however it remained in another room. So this does explain why problem is upstairs only as the 2 floors are not connected with metal stud. Hunting on...
 
so let me get this straight.....

we have random voltages to metalwork and pipework throughtout the building. Bonding some bits doesn't affect other bits and it all depends on the load on multiple circuits?

Do I recall right this is a PME system?


Have we really ruled out the MET floating relative to the true mass of the eath?
Was it ever tested against a earth spike (not connected to anything else) with load on all the circuits? I got the impression it was but was confused what the results were........
 
It was implied that the DNO had done such a test but I did re-ask the question and so far no explicit answers have been given. I was trying to rule it out but agree that we can't yet do so. However we do have numerical answers for insulation resistance that include some strange failures.
 
It was implied that the DNO had done such a test but I did re-ask the question and so far no explicit answers have been given. I was trying to rule it out but agree that we can't yet do so. However we do have numerical answers for insulation resistance that include some strange failures.

yes, it was your post I was picking up on really.
As to IR readings, again - I agree it must be significant that there are so many low results. Even the cooker I would class as low for the type of circuit!

I don't suppose the house is on a flood plain is it?
 
Guess that's the end of that. We will never know what problem was found

I think we're getting to the bottom of it.
The new build, as it was then, was ruffed in by a sparks, through the metal stud work, without protective grommets. The cables have now worn through and the phase is making fortuitous contact with the metalwork. Give it a few more months and we'll have a S/C.

Now how many circuits have been affected so far?
Upstairs lighting
RFC

Looks like a bit of a rewire.
 
I'm mightily cynical about this whole business: You've conducting water in a plastic pipe, attached to a plastic trap, attached to a plastic shower tray or porcelain bowl, sat on a wooden floor which is pulling enough current from some chaffed cable in a stud wall somewhere meters away that's sufficient to produce a tingle yet doesn't upset an RCD......

OP - I apologise, genuinely, for being this cynical, but it's just all a little too improbable! However, I do also hold a belief in the scientific approach which states that in any given problem, when ALL other possibilities have been removed, whatever remains - however implausible - has to be the truth.
 
However, I do also hold a belief in the scientific approach which states that in any given problem, when ALL other possibilities have been removed, whatever remains - however implausible - has to be the truth.]

Lol, cyncical? I should coco .........

Picard: Come back! Make a difference!
Kirk: I take it the odds are against us and the situation’s grim.
Picard: You could say that.
Kirk: If Spock were here, he’d say that I was an irrational, illlogical human being for going on a mission like this... Sounds like fun!

He is !
 
Just going to be right out there and chuck an idea in, is it any water or is it hot water, maybe a cable in contact with a water pipe an when temp increases the insulation has broken down enough to give a small voltage, of course the longer this problem the higher the voltage (possibly) just thinking outside the box really as it's seems other than tearing the house apart
 
I had a very similar problem, which I did post up on here.
i had found some voltage inthe running water under the electric shower.
my testing concluded there was low IR on one lighting circuit, very long story short, I found the 28w 2d fitting was connected L-E, and although some supplementary bonding was present I doubled up in the old fashioned places, retested after, and it was gone, I suspect just doing the light repair would have solved it.
the IR readings were still fairly good, nearly 2M ohm, even with the light connected wrong
 

Reply to Voltage in shower waste! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
316
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
962

Similar threads

  • Question
I went to look at a job like this a few years ago. My customer had a rental house, where there was an upstairs bedroom that had a newly built stud...
    • Informative
    • Like
2
Replies
15
Views
3K
Question 1 do you prefer buttered, salted or sweet salted? I'm guessing salty 😜 1. Auto range multimeter (used on mains before when testing the...
Replies
2
Views
615

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top