Hi All,
I am at my wits end here so here goes...
On Monday I was called to a domestic premises with reported shocks occuring while the client was taking a shower. This was apparently first noticed over 2 weeks ago!
We proceeded to do all the relevant checks on Earth Bonding and various testing including IR on all circuits. Most circuits proved to be fine apart from a high Zs (3.06) on the upstairs ring. All bonding was proved to be sound. Install is a PME with a split board with only 1 RCD. Main incomer has a Zs of 0.26. I moved all circuits over to RCD protection to see if any tripping would occur....to no avail.
Upon further investigation we ran a lead out from the board to provide a means of testing in the shower...what is clear is that a voltage of 6v can be meaured between Earth and the actual water in the shower tray but ONLY WHEN IT IS DRAINING THROUGH THE WASTE! This voltage increases to around 18v at least as load is increased around the house.
Upon FURTHER investigation I have now discovered this to be the case on all 3 showers and all basins upstairs. With the basins I actually filled them up, released the plug then could measure the voltage as the water drained...NOT BEFORE. With the showers I ran the water and turned off then measured the voltage again as the water drained. All showers are hot and cold fed with no local pumps.
I have had every circuit apart and individually connected 1 circuit at a time in the board and found that 4 out of the 6 circuits seemed to bring about the voltage. I have also bizarrely placed a lead between the mixer taps and into the water in the plug hole while running the water. This always removes the voltage.
I am left with the only answer that somehow a voltage is finding its way through the waste water and once someone gives it a path then the shock occurs!!
I have had SSE out today checking everything their end....no problems. Contacted the NICEIC...no advice could be given! I've consulted 2 of my so called guru electricians who are stumped. I am hoping that tomorrows investigation of the external wiring will reveal something but I'm not holding my breath!
Somebody please tell me they have come accross this before!!
I am at my wits end here so here goes...
On Monday I was called to a domestic premises with reported shocks occuring while the client was taking a shower. This was apparently first noticed over 2 weeks ago!
We proceeded to do all the relevant checks on Earth Bonding and various testing including IR on all circuits. Most circuits proved to be fine apart from a high Zs (3.06) on the upstairs ring. All bonding was proved to be sound. Install is a PME with a split board with only 1 RCD. Main incomer has a Zs of 0.26. I moved all circuits over to RCD protection to see if any tripping would occur....to no avail.
Upon further investigation we ran a lead out from the board to provide a means of testing in the shower...what is clear is that a voltage of 6v can be meaured between Earth and the actual water in the shower tray but ONLY WHEN IT IS DRAINING THROUGH THE WASTE! This voltage increases to around 18v at least as load is increased around the house.
Upon FURTHER investigation I have now discovered this to be the case on all 3 showers and all basins upstairs. With the basins I actually filled them up, released the plug then could measure the voltage as the water drained...NOT BEFORE. With the showers I ran the water and turned off then measured the voltage again as the water drained. All showers are hot and cold fed with no local pumps.
I have had every circuit apart and individually connected 1 circuit at a time in the board and found that 4 out of the 6 circuits seemed to bring about the voltage. I have also bizarrely placed a lead between the mixer taps and into the water in the plug hole while running the water. This always removes the voltage.
I am left with the only answer that somehow a voltage is finding its way through the waste water and once someone gives it a path then the shock occurs!!
I have had SSE out today checking everything their end....no problems. Contacted the NICEIC...no advice could be given! I've consulted 2 of my so called guru electricians who are stumped. I am hoping that tomorrows investigation of the external wiring will reveal something but I'm not holding my breath!
Somebody please tell me they have come accross this before!!