I did ask the question and claims not to have touched anything else, other than the CU. Which also seems to be confirmed by what the occupants are telling me.
Take onboard murdochs advice and let us know how you get on.
 
But I don't think the OP does though. lol
I do agree, I tend to only perform the r1+r2, confirm the switching, then IR it.
But as this is a special occasion, I shall on this occasion be performing additional tests on r1+rN and r2+rN. Before we start breaking parts of the circuit down.
 
Pain, pain & more pain. I had one of these the other day. Eventually traced it to a borrowed neutral AND a pinched cable. The frustrating thing about these faults is they can be so time consuming to find but the only way is to start from the beginning and test from point to point in my experience. A customer told me the other day that a guy from SSE spent three days testing in their house to find a neutral fault. Good luck mate.
 
I do agree, I tend to only perform the r1+r2, confirm the switching, then IR it.
But as this is a special occasion, I shall on this occasion be performing additional tests on r1+rN and r2+rN. Before we start breaking parts of the circuit down.

Special occassion?? You have voltage readings that suggest a lost neutral or earth, so checking continuity of ALL cores from the board to the accessories is the only step to make, this time, and every time you come across these situations.
 
Special occassion??
As this fault is new to me, that is why I asked the original question, it's an historical fault, not something I have introduced and required some help on fault finding and diagnostic. Which I grateful that you have offered.
 
Pain, pain & more pain. I had one of these the other day. Eventually traced it to a borrowed neutral AND a pinched cable. The frustrating thing about these faults is they can be so time consuming to find but the only way is to start from the beginning and test from point to point in my experience. A customer told me the other day that a guy from SSE spent three days testing in their house to find a neutral fault. Good luck mate.
Well hopefully experience will put me in a more informed position next time.
 
You have voltage readings that suggest a lost neutral or earth, so checking continuity of ALL cores from the board to the accessories is the only step to make, this time, and every time you come across these situations.
As I stated in OP, if I test across switch live and neutral on a closed circuit I get 240V at all fittings, which would suggest that the neutral is present. Unless as mentioned the neutral is borrowed/shared or returning via they earth.
I am unsure what you mean be lost with regards to this.
But I am grateful for your input, is it possible that the fault has been introduced via damage between conductors of two differing circuits and therefore also testing for that,via IR tests across differing circuits.
 
Last edited by a moderator:
Pain, pain & more pain. I had one of these the other day. Eventually traced it to a borrowed neutral AND a pinched cable. The frustrating thing about these faults is they can be so time consuming to find but the only way is to start from the beginning and test from point to point in my experience. A customer told me the other day that a guy from SSE spent three days testing in their house to find a neutral fault. Good luck mate.

A pain maybe, but for someone that's familiar with fault finding in a methodical manner, that understands the values being shown to him by his test equipment, can sort these sort of problems out pretty quickly, even double fault problems!! Alas the above only comes with experience, and there is no substitute for experience!!!
 
What readings do you get with the cpc conected
I was wary of connecting the CPC, as there was a young family in the house and some accessories were metallic. Also I would have expected the RCCB to trip, if any leakage to earth. So a reading was not taken, I am waiting for response from the client with regards of continuing the work, so as yet I have not been back to the job.
 

Reply to Voltage reading puzzle in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
401
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
989
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Induced voltage can be a bit of a red herring when using DVM my guess is somethings moist.
Replies
5
Views
470
TerryBNZ
T
  • Question
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
Replies
9
Views
776

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top