Voltage Stabiliser | Page 4 | on ElectriciansForums
Discuss Voltage Stabiliser in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Even before the PV's were installed, the voltage was pretty high. The machines have 3P motors, and the control gear is 24V. Would the 24V PSU be affected by the incoming voltage fluctuating?
3p motors? 3 phase?
is the 24v DC or AC?
What sort of PSU is it?
you will also find that such devices are rated at 230v, as is the same with all electrical equipment throughout the UK and Europe.
They are designed with this in mind taking into account the respective tolerances
3p motors? 3 phase?
That would depend on how old these box making machines are. If manufactured pre harmonisation, eg 220 Volt generally with a typical +/-10% tolerance. Running at 240 volts will be at the very top end of that tolerance, and if there seeing closer to 250 volts, ...not very good at all!!
When can we get rid of the myth of 230V?
The specification for new distribution transformers is 11/.433KV. NOT 11/.4KV
for the rest of us that dont deal with transformers.
i know there is 400kv,33kv,11kv,415,230
is it only below 11kv that the voltage spec changed due to harmonization
400KV
275KV
132KV
33KV
11KV
3.3KV
660V
550V
433V
There is also 66KV in the northwest and 6.6KV in parts of London.
Voltage regulation with OLTC’s is usually at the 33/11KV level.
Forgetting about the 6.6KV supplies, as they are pretty rare these days, you'll only generally see 33KV and 11KV being transformed to a LV distribution. The higher KV rated systems being used for transmission duties over long distances. By far the most common local distribution is 11KV for supplying the DNO's LV distribution networks...
Reply to Voltage Stabiliser in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
These are questions to complicated for a simple answer It depends on many things Cable size Cable length Load type and current Filtering and...
The cable is way undersized. If the voltage drop is detrimental to the installation I would make a mention of it as volt drop generally is not...