Hi all,

I have install a RCD fused spur on the end of line feed to a bathroom lighting circuit. Thus protecting the bathroom with rcd.

I tested the rcd (manually via the push 'test' button) and it killed the lights and fan as expected.

I used my volt stick to confirm that the cables were dead, but to my surprise , The voltstick was telling me the there was voltage still present. How could this be?

My understanding was that with the RCD tripped, it should kill all power on the load side of the spur, .

Any ideas????

Thanks
 
...This debate is circular,as approved test gear aside,ADDITIONAL equipment is at the testers discretion.Surely folk cannot be "against" a device,only its' particular use in any one instance. Personally,i chose to give my volt-stick type yokes away,but only because i got a Megger dcm330,which had a built in volt detector in the head of it,and i prefer devices which have more than a single function.It has proved to be a VERY useful item of equipment. Condemning chaps for ownership of volt-sticks is pointless,WITHOUT knowing what they do with them.Even if it is amusing the children...When i was a teenager,i worked on a local farm,where the owner,and his son,would use divining rods to grid out any proposed land drain,before we got the excavator out.All i know,and science has helped to form me,is,it worked. I reckon you would still have a fight on your hands,to convince the son,not to continue with those rods,before each dig....just off to "throw the bones",to see what my future holds...:thinking:
 
Hi all,

I have install a RCD fused spur on the end of line feed to a bathroom lighting circuit. Thus protecting the bathroom with rcd.

I tested the rcd (manually via the push 'test' button) and it killed the lights and fan as expected.

I used my volt stick to confirm that the cables were dead, but to my surprise , The voltstick was telling me the there was voltage still present. How could this be?

My understanding was that with the RCD tripped, it should kill all power on the load side of the spur, .

Any ideas????

Thanks
Really!?
A voltage stick is not appropriate in this situation. You may as well wave your dick around to indicate voltage.
 
Last edited:
I agree that they are only truly 'safe' in the hands of experienced sparks who know what not to use them for. Horses for courses. But they can be exceedingly useful and quite reliable if you know their foibles.

A few of us here often work in the dark, in silence, under pressure and/or up high structures, so something that will fit in a pocket and lights up clearly is a bonus. A non-contact indicator is a must. How else would you find which of 12 runs of flex is faulty, at which end and whether it's the line or neutral that is O/C, in darkness and without opening any connectors? 12 seconds with a voltstick, impossible with a DMM or MFT.

I gave one to an electrician in Russia 20 years ago. He had never seen anything like it and was delighted with it, but immediately understood what it could and couldn't do. I expect he still has it.
 
I got one given by a rep in a wholesalers a while back. I waved it over a damp piece of wood in the rear storage yard of a pub I was working on. It indicated it was live.
I threw it away.

Christ!! I'd throw a live piece of wood away as well Trev!
 
Last edited:
I agree that they are only truly 'safe' in the hands of experienced sparks who know what not to use them for. Horses for courses. But they can be exceedingly useful and quite reliable if you know their foibles.

A few of us here often work in the dark, in silence, under pressure and/or up high structures, so something that will fit in a pocket and lights up clearly is a bonus. A non-contact indicator is a must. How else would you find which of 12 runs of flex is faulty, at which end and whether it's the line or neutral that is O/C, in darkness and without opening any connectors? 12 seconds with a voltstick, impossible with a DMM or MFT.

I gave one to an electrician in Russia 20 years ago. He had never seen anything like it and was delighted with it, but immediately understood what it could and couldn't do. I expect he still has it.

I doubt it very much Lucien as the early RS/MK models available at the time broke as soon as they were dropped on the floor as they always seem to land tip down first which resulted in a broken tip.
 

Reply to Voltage still detected after rcd had tripped? why could this be... in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Ok I’ll try this when I’m down
Replies
4
Views
398
  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
693

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top