Oh and to clarify as well when I switch off the breaker to this circuit only the earth voltage disappears
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Voltage up to 100v on CPC even when disconnected in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
i have spoken to the second man and he has admitted to me that he tried to take an earth loop but the tester wouldn't let him
Oh and to clarify as well when I switch off the breaker to this circuit only the earth voltage disappears
Yes oh dear I have dealt with the issue accordinglyOh dear!, so instead of investigating this issue (above 50V touch ?), the installation was put into service with a possible inherent defect.
so, the stray voltage must be coming from that MCB. dis all that circuit's cables from CU. do continuity and then IR tests on that circuit with all loads disconnected. bet you the IR tests will show a L-E fault on that circuit.
Oh and to clarify as well when I switch off the breaker to this circuit only the earth voltage disappears
so, the stray voltage must be coming from that MCB. dis all that circuit's cables from CU. do continuity and then IR tests on that circuit with all loads disconnected. bet you the IR tests will show a L-E fault on that circuit.
not if the fault is transmitting through a load to N and then onto the earth via the TNC-S.
I would be more concerned about how the Earth is rising above 50V, and why the ELI test could not be performed first and foremost, then try to find the other fault.
Something doesn't add up here, I would be inclined to start re-testing from the beginning.
TN what though ? TN-S or TNC-S...
Reply to Voltage up to 100v on CPC even when disconnected in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net