I like a bit of fault-finding.
I plan to be in Guildford tomorrow. PM me if you like and I may be able to put a second pair of eyes on the job.
I then disconnect all the cpc's from each other at each switch (fed at switches not 3 plate) I still have voltage on the earth on the incoming and outgoing feed even though they are disconnected from each other
I wouldn't mind betting that at least one fault, is in one of the switch back boxes that's jammed packed full of cables!!
Re: Voltage up to 100v on CPC even when disconnected
Originally Posted by spark 68
Oh dear!, so instead of investigating this issue (above 50V touch ?), the installation was put into service with a possible inherent defect.
Yes oh dear I have dealt with the issue accordingly
How, may I ask?​
TNC-S sorry forgot to answer that
OK. I think it's worth checking the supply first. If that's not right, nothing else will make sense if you're live testing.
What's the resistance between incoming neutral tail to the CU main switch and the earth bar in the CU?
And worth checking polarity on the supply. Does a volt stick light up on the line, but not on the CU neutral or earth bars?
I cracked it
the problem was actually quite simple in the end, the solution was a bit tougher though
i approached it as a new installation and tested the whole lot, turns out the guy who said he'd done r1 + r2 obviously hadn't
there was a break in the earth somewhere in the circuit leaving most of the lighting circuit unearthed!
with no earth the cpc was getting endured current from the live
couldn't find the break in the earth but managed to refeed the circuit from the board!
thanks to everyone for the helpful advice I'll try and return the favour in the future
Trying to do a Zs on the circuit may have helped highlight the fault. Worth remembering for future.
I cracked it
Another valuable lesson learned, ... ''Never'' take as gospel what others tell you, Always check for yourself!! That is especially the case when in fault finding mode!! lol!!
Had this sort of induced current before with similar voltages.
What you have to factor in is not just the voltage but the current behind it too.
It may well be 100 odd volts or so but may only be milliamps 'worth..
Satisfy yourself that it's all compliant, that OCPDs and RCDs are working correctly then, let the earthing system do it's job and dispose of it.
chrisses,
GT1,