I do? New on me, but I will give it a try. When the current is over the rating of the fuse. I got 10/10.

Nope. They will hold at over the rated current for quite some time. But you were close.

What they won't do is rupture when there is a loose connection. A loose connection does not cause an increase in fault current through the fuse.
 
Socket outlets terminals are designed to take multiple conductors, the terminals are fixed and they have gone through a testing process to comply with BS1363
Two solid core cables in a socket, FCU's, etc, terminals is not a good thing at all. When pushed back, stress is on the wires/terminal. I have come across many that fell out when a socket was removed - they were tight before the socket was pushed back. The screws also work loose over time with expansion/contraction. Unlike Maintenance free Wagos. Two cables are never in a Wago terminal. One flexible cable is far superior into the rear of a socket/FCU etc. It just is.

I never suggested using Wagos in appliance grids. Another poster pointed out the clustering on a ring, or radial of a dedicated appliance switching module.
 
Last edited:
Two solid core cables in a socket, FCU's, etc, terminals is not a good thing at all. When pushed back, stress is on the wires/terminal. I have come across many that fell out when a socket was removed - they were tight before the socket was pushed back. The screws also work loose over time with expansion/contraction. Unlike Maintenance free Wagos. Two cables are never in in a Wago terminal. One flexible cable is far superior into the rear of a socket/FCU etc. It just is.

Now that is the first post of yours which I agree with. Well, mostly anyway.
 
Your method will probably never cause an issue....

My initial point was that the internal bus bar in a Wago can be used to take off a few Spurs from the Wago, when on a ring circuit. Below: the bus bars can be clearly seen on a three connection Wago (left) and a four connection In-Sure connector on the right.
Ring in and out of the end connections, making the bus bar a part of the ring, then two spurs off that, using the middle connections - all legal.

[ElectriciansForums.net] Wagos on Final Ring Circuits
 
My initial point was that the internal bus bar in a Wago can be used to take off a few Spurs from the Wago, one a ring. Below the bus bars can be clearly seen on a three connection Wago (left) and a four connection In-Sure connector on the right.
Ring in and out of the end connections, making the bus bar a part of the ring, then two spurs off that, using the middle connections - all legal.

View attachment 63948

It makes NO difference AT ALL whether you use the outer position or the one next to it. The connector is rated for the specified current. 5mm of copper makes virtually zero difference.
 
Yep, I agree that sometimes connections can work loose if people are careless. Always push the socket back, then re check the screws are tight before final fix.
That is time and effort. Then there is the prospect of the terminal screws loosening over time - happened on one of mine, an FCU supplying a dryer. The ring's current runs through those socket terminals, which is not a good thing.

Having the ring run through a maintenance free Wago in the back box, with a felxible cable into the sockets from the Wago is a far superior solution. The Wagos connections take the current load around the ring, not working loose over time. The ring's current flow is kept away from the socket's terminals. Current only flows through a sockets flex wires and terminals when the socket is switched on drawing current. Superior, safer and quicker solution.

In Germany they sell sockets with Wago connections on the back, making matters even easier and safer.
 
Last edited:
Each spur has its own connection on the Wago, taken off the internal bus bar, not taken off one connection.
Look at the photo.
Its not a busbar, its a connector with multiple cable outlets.
I know you keep referring to the solid continuous piece of metal inside of the wago as a busbar, I get it, it even functions like a busbar. But its not a busbar its a connector, thats it's purpose and thats the standards its been tested too. If you want to convince me that wagos are busbars then your need to show us the relevant BSI documentation.
 
Last edited:
@AJshep please be careful not to get sucked into this thing now! By condensing each point into just the width of one port on a Wago 221, it seems the OP managed to wire up an RFC smaller than its own Schwarzschild radius and it collapsed into a black hole. This is now pulling cables, sockets, junction boxes and possibly electricians too, across its event horizon. As the materials accelerate away from us, the Lorentz-Fitzgerald contraction makes cables look like busbars and busbars look like single terminals. Due to gravitational lensing it is no longer even possible to distinguish a ring from a spur.

The singularity beckons...
 

Reply to Wagos on Final Ring Circuits in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
I've made the required tweaks on the junction box with a 4mm hole bottom, upturned wagos and reduced the exposed copper. I did originally install...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top