So I am doing an insulation resistance test on a new flat and I get a dodgy L-E reading on the IR. I won't go above 20Meg and it fluctuates. Identified where the problem is and its a switched spur. When cables are removed all test +299 including the load which is 2 sockets. When all are put back in spur, the load gives the same dodgy reading. Replaced the spur and still get the reading. Any thoughts?
 
Load side L leaking to real earth but not to its own CPC, which is well insulated from earth. So you only see it when supply and load CPCs are connected together. Try testing between load L and supply CPC with the FCU removed.
 
Re#7: I may be a but thick today (in pain with my new knee after its total replacement) but should your explanation read:

'you only see it when supply and load Ls are connected together.'

Then your final sentence makes sense.
 
I prefer my version. Suppose the load L is damaged somewhere along the cable and leaking to the building structure or ground, but the CPC is not in contact with ground as the fittings are in dry studwork. Measuring L-E in the load cable alone will not reveal the fault due to the floating CPC. But the supply CPC, in contact with the building and ground through the bonding / main earthing, will be connected to the fault. Thus when the FCU is installed, even with the switch off the load cable will now read faulty as the CPCs are connected together.

BTW good luck with the knee. Do the exercises! Gave my mum her mobility back, has been marvellous, after ten years she can't tell it's not her own.
 
I think a take-away from this interesting problem is the importance of not only doing pair-wise IR readings for the supply cable and then the load cable but also to do the cross-pairs between conductors of the supply and load cables .
 

Reply to Weird IR results? At a Switched Fcu in RFC in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
971
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K
  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top